I recently had to change the way my MSG instructions were connecting via ethernet radios; I originally had the remote PLCs in the I/O of the "master" PLC, but it was crashing the connection because of too much data. The solution was to manually tell the MSG instruction where to connect not by "browsing" to the I/O list, but rather to type out the IP address of the remote PLC.

The string in the path line at the "master" PLC is:

Code:
LCP_W_Ethernet, 2, 172.16.254.20
where:

Code:
LCP_W_Ethernet - name of the master PLC's ethernet module
2 - something to the effect of "go out to the ethernet"
172.16.254.21 - IP address of the remote PLC
Can someone clarify what that '2' means, and what (if any) other options there might be? I read that simply "it should always be '2'" but want to make sure things are set up correctly. I did a decent amount of searching for Rockwell Technical Documents that might describe this path, but couldn't seem to find anything that described manually creating the path (as opposed to adding the remote PLCs to the master's I/O).

Oh, and this is a master ControlLogix to a remote CompactLogix.

Thanks!
 
Last edited:
CIP Path segments generally consist of a pair of values: a Port and an Address.

The name of the ControlLogix Ethernet module is shorthand for the first segment in the CIP Path. Under the hood, that CIP Path segment is "1, Slot".

In fact, if you typed this in as "1, x, 2, 172.16.254.20", where x is the ControlLogix slot number of the 1756-EN2T module, Studio 5000 would substitute the module name when you hit Enter.

1 is the port number for the ControlLogix backplane.
2 is the port number for the module's network port.
3 is the port number for the module's second network port, if it has one. The only module I know of that has ports 1, 2, and 3 is the 1756-DHRIO.

So in short, the "2" does mean "go out to the Ethernet".

CompactLogix makes some of this more complicated, especially because ther is a difference between the way the older popular 1769-L3xE and the modern 5370 controllers work.

In your case, just treat the CompactLogix IP address as the endpoint of the message and don't put any additional "backplane, CPU" CIP segments into the CIP Path.
 

Similar Topics

Hi! So my problem is a little funky, I had Studio 5000 v 24 and 30 installed, but forgot to install RSLogix (which I cannot go without). Is there...
Replies
2
Views
123
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
Replies
15
Views
428
I'm a Siemens person, and this is one of my first AB programs. The customer wants everything programmed in Ladder. I have a lot of data (3...
Replies
14
Views
223
Good day everyone. if you have a logic for 3 pumps (lead/lag/off), would you please email it to me? I really appreciate it!
Replies
7
Views
220
Maybe this is just not possible, or maybe I am doing something wrong. Background; I have a data array of over 1500 products. For sorting I...
Replies
6
Views
765
Back
Top Bottom