M221 and SoMachine Basic - Indirect Addressing?
Saffa
Feb 2012
Bay of Plenty
1,468
Hi All,
First project using the Schneider M221. Simple valve control where I have to open a valve to a fixed position depending on time of day. There are 17 different "time slots".
What I was hoping to do was simply build an array of valve positions, and step through it using a timer. After the timer expires, move next timer value into present, move valve position from array to valve positioner. Re-sync to RTC once a day (accuracy is not super important).
If I had a Micrologix I'd use indirect addressing. I can't seem to find anything similar for the M221? The drum instruction is laughable - only 8 steps!
I can brute force it but it's just nasty. This is only going to be running this system until summer when we can get a proper system installed.
Thanks!
Look from M221 help indexed addressing.
%MW200:=%MW100[%MW0] on operate block is syntax.
%MW0 = 0..17
-> %MW200 have values from words %MW100.. %MW117
You can use words only
p.s 17 different times :unsure: Would it be easier use 24 (hours) directly to index if accuracy isn't important?
Awesome, thanks Lare.
Yes it's silly I know. I think the accuracy is not that important but our process engineer is one of those "in theory" kind of people. 80% of the time the valve changes position on the hour, the other few hours the transitions occur at varying times within the hour. I have 3 graphs and a very big excel table provided as proof of his reasoning.
So adjustable look up table is easiest then he can spend days tuning this thing in the snow, while i sit back at the lodge 🍻
hmm, how you program it indirectly. Brutal compare method would take some 18-20 rungs with PLC clock.
With timer and count up, and ajusting it every day it isn't much shorten to program
I'm still using the PLC clock, not a timer. Using indirect reference only took 6 rungs for the counter, compare and move logic for the valve position. All good, thanks for your help
Hi all, I've been trying to develop modbus rtu program between uv balasts and plc ı'have 6 slave balast.I am reading fault run voltages etc...
1,206
Hi Guys, I'm using M221(TM221CE24R) PLC and SoMachine Basic from Schneider and having a bit of problem. 1. I can't able to read the data from...
1,751
Hello! I am new at PLC programming. I am using TM221CE16R PLC with TM3AI8 analog input module and SoMachine Basic v1.6. I am trying to scale...
7,103
this is my first time using this software,trying to scaling PT100 (scale unit -2000~8500) using simulator but the result so funny,can somebody...
2,456
Hi All, I am a newbie to Modbus tcp communication, and need some directions in this regard. I have TMCE221CE16R with SoMachine Basic as my...
5,481