The above HMI does not power up and is located on a Caribbean island. This started after a 24 hour power outage. It has power now but the screen is black. We will have it shipped to the mainland overnight. We have the software to program but do not have the application file to load onto a replacement. I wonder what our options are. Can the unit be repaired and/or application be transferred to a replacement of the same model? The OEM is no longer in business. We have about a week turnaround and want to consider the best path forward.
 
This is an obsolete model, but if you can upload the editor project it's possible to put it into a more modern panel. That is however completely reliant on the panel still being alive enough to upload the editor project, and assuming the original integrator ticked the "Include Editor Project".

If not, you're starting from scratch.

This model has a green LED on the front to indicate its powered. Is that light on? If so, hopefully it's just the backlight that has failed.
 
Thx...Can anybody recommend a repair company (not sure if this is acceptable on this forum)? I've had mixed results doing this.
 

Similar Topics

I am having trouble running the application throught my PLC, tm221me32tk with magelis HMIGTO6310 I have prepared the plc programme, also created...
Replies
0
Views
111
Good morning friends. . We are having a problem with one of our machines that have two HMI consoles connected to the same network. They have...
Replies
0
Views
1,124
I am looking at a bakery oven that has been dismantled and in storage for unknown time, it was manufactured in 2012 so not that old. my gig is to...
Replies
8
Views
3,620
Any regular users of the magelis range? If so, anyone have a slick way to do a common popup with a rockwell UDT? My current approach is to just...
Replies
3
Views
1,656
We're a second hand machinery merchant. We've just had a machine arrive that has a Schneider Twido TWDLCAA24DRF PLC and a Magelis XBT-R411 HMI...
Replies
4
Views
2,402
Back
Top Bottom