Let me see if I have some key points right...
1. The original problem was the feeder valve went too fast and caused line plugging.
2. This was solved by using a VFD to slow it down to an acceptable feed rate.
3. Everything works fine if you leave the feeder valve at this speed.
4. You have a problem with bags running out.
Conclusions
1. Do not try to control the feeder valve speed. It doesn't do anything good for you. If it's too fast, the line plugs (the orginal problem) so why install controls that let it go too fast?
2. The problem with bags running out is completely unrelated to feeder valve speed. I can see where a beacon light that comes on if the discharge pressure is low and the feeder valve is running for a couple minutes would be helpful to let the operators know that the bags have run out. I can also see shutting down the system automatically if say 10 minutes go by and no one hangs another bag.
3. What happens if the silo fills up? You may need a high level switch so you can shut the feeder valve off before you plug the line. Or if the operators know the level, they can just avoid hanging enough bags to fill it. That's probably OK if the silo is relatively large.
1. The original problem was the feeder valve went too fast and caused line plugging.
2. This was solved by using a VFD to slow it down to an acceptable feed rate.
3. Everything works fine if you leave the feeder valve at this speed.
4. You have a problem with bags running out.
Conclusions
1. Do not try to control the feeder valve speed. It doesn't do anything good for you. If it's too fast, the line plugs (the orginal problem) so why install controls that let it go too fast?
2. The problem with bags running out is completely unrelated to feeder valve speed. I can see where a beacon light that comes on if the discharge pressure is low and the feeder valve is running for a couple minutes would be helpful to let the operators know that the bags have run out. I can also see shutting down the system automatically if say 10 minutes go by and no one hangs another bag.
3. What happens if the silo fills up? You may need a high level switch so you can shut the feeder valve off before you plug the line. Or if the operators know the level, they can just avoid hanging enough bags to fill it. That's probably OK if the silo is relatively large.