math used to determine level of water in a tank
micro
Feb 2004
need to know how to determine how much water in a tank by taking the MA output of a transmitter and converting it to feet of H2O.
thanks
It is a pressure transmitter the tank is a ground storage tank with the pressure line coming off the bottom of the tank it is 45 ft tall with a capacity of 8 MG of water.
What is the range of your transmitter. The most common ma range is 4 to 20 ma. What does 4 ma=? and 20 ma= ? If yours is different what does the high and low equal
You first must know what your milliamps represent in terms of engineering units.
Here is an example:
The most common ma range is 4 to 20 ma, so let’s say this represents 0 to 100” H2O
Where 4 ma = 0”H2O and 20 ma= 100”H2O.
(((Raw ma – 4)/ 16) * 100 ) / 12= 4.167 ft H2O
As Mickey points out, you need to tell us more about both your transmitter and your PLC's analog inputs. I'm assuming you're wiring that 4 - 20 mA signal to a PLC's analog input. You didn't specifically say so, but this is a PLC site.
First, you're measuring pressure to a maximum depth of 45 feet of water. What is the maximum range of your transmitter? Can you calibrate it so that it outputs 4 mA at zero depth and 20 mA at 540 inches (45 feet)? Pressure increases with depth at the rate of 1 PSI for every 27.68 inches. The pressure at the bottom of a 540 inch tall (full) tank will be 19.5 PSI (above atmospheric). If you're using a transmitter rated for 0 - 20 PSI, you can probably calibrate it as I indicated above. If you're using a transmitter rated for 0 - 50 PSI, you will end using less than half of the transmitter's available range.
The next point you need to consider is the PLC's analog input. Are you using a 12-bit or a 16-bit analog input? A 12-bit analog input divides the the 4 - 20 mA range into 4096 steps. A 16-bit analog input gives you 32,768 steps. For a 12-bit AI, each incremental step represents a little over 1/8 of an inch (0.13") or 1953 gallons of water.
Then once you get the height of the liquid in the tank by converting the pressure input as Steve said, then you can use the standard volume of a cylinder formulat to calculate the volume in gallons or whatever, V = 2 x Pi x r^2 x H, where H is the height and r is the radius or the tank.
micro said:
... with the pressure line coming off the bottom of the tank...
If that is an electrical signal line, no problem.
If that line is actually a tube filled with water, then you need to locate the pressure transmitter at the same altitude as the bottom of the tank.
that is correct the pressure range is 0-20 psi 4= 0 ft. and 20= 45 ft. thanks for you info. micro
I am an old man who can't remember much when it comes to geometry. I am trying to calculate the numbers on this diagram. I have drawn them in...
22
5,505
2,182
have posted a section out of a program that a integrator did for one of our plants in mexico. Now the integrator has busted up, and the company no...
3,169
I have an expression in a structured text routine of a Logix controller that looks more or less like the following: ResultInteger := Integer1 *...
398
This application has a motor with encoder feedback that drives a linear actuator that moves in/out, and is at roughly 45 degs from horiz. As the...
19
1,372