The literature states "128 axis _CIP_Drive configurations based on Ethernet TCP Connections. Of those 128, 8 Position loop axes maximum." Does this mean I can have a max number of 8 or some number up to 128 drives on the 1756-en2t with l71 processor. This is for a 3 to one merge conveyor system.
I currently have (8) 755 drives and (4) 525 drives on a single 1756-en2t and started experiencing faults.
Hi
What are the faults you are getting. What Processor are you using and what firware is the cpu and the Ethernet card. With the current number of vsd's you should have no problems as I have carried out much larger installs with no errors once I get it running
Donnchadh
All the drives are shutting down with F73 code. Processor is an L71. Not sure on the firmware v, if that is critical I can find out, but it was installed in the last 6 months.
ethernet running from en2t card to eds-516a managed 16 port sw, indiv drives are connected to ports on the switch. Drives are all under 25' to the indiv motors.
thanks
PowerFlex AC Drives: Port Adapter Faults F71, F73,F75 or F76
66126 | 01/13/2010 | Access Level: Everyone
Originally posted by rdrast:
That is an adapter card fault.
Unless he is referring to the PF525's, in which case it is an embedded Ethernet port comm loss fault.
You are down to three components:
the EN2T, the switch and the cable between them.
Cables are easy to change; I would start there.
If you access the EN2T webpage there is a diagnostics section that will tell you what the loading is on the EN2T. You might want to check that but I really believe it will show a very low percentage of loading.
There really isn't much the plc can do you cause a loss of comms to all the drives but I may be wrong there.
And then there is the switch. You might want to see if the switch serves up a webpage with any kind of information.
Keith
Hi
I would start by removing the managed switch and use an unmanaged switch.
I would also check the cables.
Is this a new install or has it been working?
Donnchadh
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
157
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
234
Square-D Symax SFI-324 I have used the SFI-510 card for many projects, but I came across a SFI-324. Does anyone have ant tech info on it?
87
Hi, I am looking for some help with a GE Fanuc Versa Max Micro Controller model IC200UDR001-BF connected to a Quickpanel mini display...
167
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
145