When I converted the PV1200 to ME for a PV+, Most of the addresses I can go in and change to the appropriate block transfer. But with the binary and integer block transfers that use part of a word, it is difficult to convert. Is there any examples out there to see how it is done?
So you must still be using RIO on the PV+? I've heard RIO on PV+'s is a pain. I know Ken has done this, maybe he will add his expertise. I've managed to avoid doing this so far?
I believe that you can use the bitshift commands in the tag formula to use the bit that you want, bitshift in one direction and then the other to get the bit that you want.
I cannot find an example now if I find it I will post it.
Alan
There are a handful of approaches, most of them involving Expressions. Version 5.0 and later did give you some more flexibility with Aliases, too.
Related Knowledgebase documents: 26150, 27079, 27284, 31043.
If you don't already have your hardware, be aware that the v6 hardware will not support RIO adapter mode with the 2711P-RN6. As I understand it the three "I/O Connection" modes were dropped from v6, which includes RIO, ControlNet Scheduled, and DeviceNet Polled.
I have not kept up with the specifics of this so you'll want to confirm for RA what is supported on your hardware (the 400/600 interface is a little different) and revision.
Hi folks, I'm trying to parse a binary string on a Red Lion DA30D using a Raw UDP/IP input port. I've done this before with ASCII strings so I do...
38
1,000
So here's my situation, I have been tasked with modifying the logic to mimic a button press in the PLC. I have two identical machines however one...
551
Hi, I want to extract every second bit of a double word and place it in a new word but the position of placement should be from 0,1,2......15...
17
3,101
Hello, I am trying to convert a incoming string that is in Binary format (See attachment) to a DINT. Any ideas? When I use the STOD command it...
2,230
How can I read individual binary bits from a SLC500 within FTH SE? With the Tag Browser I can get to the Binary Files and get each Integer from...
1,611