.mer and .apa Panel View

Searched for the Tag in the 500 project, (PHECoolControl\perc_open) N19:85 for the cold side, and Tag (PHEHotControl\perc_open) N19:39 for the hot hot side. Neither one was found.
 
Go to help, SCL Instruction Help choose PID. then click on
PID Control Block Word 16 is Control Output 0-100% So The Tag N19:85 is coming from CG1 PID whose address is N19:69 + CV = word 16 so N19:85

PHE COOL PID is N19:46 + 16 = N19:62 So Looks like Tag in HMI should be addressed to N19:62

PID_jpeg.jpg
 
I believe Something about this is not right.
How can the Cool percent control and the CG1 control have the same N19:85 tag from the PV. 85-23="62" maybe that's what they meant to program in. right?


l16percentintegerworng.jpg

line16 coolpercenta.jpg

percentcooll16correctaddress.jpg
 
I made it using the fill box on the cell. Point mouse to bottom right corner of cell. Mouse will turn into a + sign Hold down left mouse button and drag down.
 

Similar Topics

This was asked in another forum and taken down due to being a 'backdoor', but this has useful info that might be useful to someone in a pinch. I'm...
Replies
6
Views
620
Hello PLCs.NET! 1) I wanted to know if there is a way to import PVP files into ViewSE. I have the APA and the MER files. When I did an "Import"...
Replies
6
Views
2,485
So I was asked to save backup files for our FactoryTalk View SE HMIs onto a USB. Few questions: 1. What is the difference between MER and APA? 2...
Replies
9
Views
6,504
I have been working on a project where all the HMIs are windows based PCs running FTSV Station v8.2. I have studio v8.2 and so did everyone else...
Replies
2
Views
1,477
Hello I have two panelview running. I'm trying to restore project files from their runtime files. I upload the .mer file and try to restore a...
Replies
10
Views
15,412
Back
Top Bottom