Message between 2 PLC5/20 via dhrio bridge
controlled
Nov 2005
bowmanville
419
I'm trying to use a message instruction to read the value from a PLC5/20 into another. I have searched the forum, but am getting more confused.
Each of the PLC's use Node 40 as the DH+ address. They are wired into a control logix gateway utilizing a dhrio card and a ENBT card. The network works great as it is (I can go online with both controllers, and I have factorytalk view reading data from both controllers.)
From what I have read, i believe i need to use multihop messaging, but when i try to enter the MSG parameters in RSlogix, it doesnt give me the multihop option.
Any help would be greatly appreciated.
What you need to do is called "Remote DH+ Link Addressing". It's a very old Data Highway Plus internetworking technique.
First examine both PLC-5's and find out what the Link ID for each one's DH+ port is. Not the Node Number, the Link ID. This is like a "network number" that can be used to tell one DH+ network from another.
Next examine the Routing Table in the 1756-DHRIO (right click in RSWho and select "Module Configuration").
What you need to do is set up each PLC-5 and DHRIO channel that are physically connected together so that they have the same Link ID. The Link IDs for the two different DH+ networks need to be different.
Then when you send a MSG command you select "Remote" instead of Local, and enter the Target Link ID as well as the Target Address, and the address of the Gateway (the 1756-DHRIO port).
There is a pretty good example of how all this works in the 1756-DHRIO User Manual, publication 1756-UM514.
Can anyone screen shot an example message block In a Control Logix PLC to communicate to a Micrologix 1400. I tried this the other day and ended...
3,130
Hi ... Everyone* I have this warning Cicode message : " possible missing operand between tags" when compile below code 👇...
3,003
Hi, right now I have a real PLC on which i'm connected by ethernet right now, and i'd like to simulate a second PLC with RSEmulate and make...
1,533
A bit new to setting up messaging instructions but I copied another in the program. Seem to have everything set up but still comes up as a...
1,587