As a follow up, we finally got Ethernet/IP working with a router (Cisco 6K series), where the router and the switches are part of the same VLAN.
When in such a setup, the router does not decrement the TTL, if the packet's destination is in the same VLAN. However, if you try to send an Ethernet/IP packet from one VLAN to another, the TTL will be decemented by 1 to 0 by the router and the packet will not be forwarded.
I will follow up later with more information.
 
Cisco 6K - wow! This cost more than extra controllogix PLC set at remote location.

Why include this network subnets with router in it when its clearly not usable with the product and create confusion. Atleast add a sentence in there that says its a general configuration and routers will not forward Ethernet IP packets.
I did read the text.
A-B describes in manuals only supported configurations.
BTW messages can use routers and all these pictures are valid.
 
Last edited:
Contr_Conn said:
Cisco 6K - wow! This cost more than extra controllogix PLC set at remote location.

A-B describes in manuals only supported configurations.
BTW messages can use routers and all these pictures are valid.

The Cisco 6K was part of the existing network. We just had 2950s hooked up to the 6K.

That is right - the pictures (and the text too) are valid for messages.
 
Dear All
I use compactlogix L35E with IP(192.168.1.6)
With FlexLogix L34 with daughtercard with IP(192.168.1.2)
I need to read info. from flexlogix therefore I use MSG
Config. Tab is CIP Data Table Read and (Source element ..... Nu. of ele........Desti......)
Commun. Tab is (LocalENB,2,192.168.1.2)
But an error happens 16#0004, what should I do?
Thanks
 
Welcome to the Forum, Omar.

For new questions, please start a new thread, rather than resurrecting a very old one. This is appropriate even when the topics are similar.

In your case, you need to add one more "hop" to the end of the CIP Path so that the message gets from the 1788-ENBT daughtercard to the FlexLogix CPU.

The CIP Path should be:

(LocalENB,2,192.168.1.2,1,0)
 

Similar Topics

Ok I'm racking my brain on this. Maybe I'm missing something but I could really use to help. Google gave me many links to here but none of them...
Replies
11
Views
2,636
Hi, right now I have a real PLC on which i'm connected by ethernet right now, and i'd like to simulate a second PLC with RSEmulate and make...
Replies
2
Views
1,532
how do you setup a message in controllogic to read the input/output table of a plc 5, is this possible
Replies
4
Views
2,012
hi everyone, i have problem regarding Audit in FTV ver 12,In audit message "service disruption:<HMI server name>:<SERVICE NAME>" message logged,i...
Replies
1
Views
45
Is there a way to add a local message display to Studio 5000 View Designer? If its there, I’m not finding it. I have used them in older versions...
Replies
11
Views
410
Back
Top Bottom