micro 1400 major fault clear

Jeff23spl

Member
Join Date
Jan 2010
Location
Canada
Posts
860
Hello

Is their any way by the local plc button (Micro1400) to clear a plc fault without going online with a laptop?

A foreign customer would like to get back online before i can go there to find the cause and fix it...
 
You can view the fault code via the LCD on the MicroLogix 1400, in the "Advanced Set" menu. This is described on page 153 of the User Manual.

I don't think there is a way to directly clear a fault condition on the MicroLogix 1400 using the keypad and LCD.

After he has noted the Fault Code, have him try switching the controller into PROG mode, then back to RUN mode, using the LCD and keypad. This frequently clears recoverable faults in SLC controllers but I'm not totally sure about the MicroLogix 1400.

If the fault is a programmatic one like overflow of an indirect address or a negative number in a preset that doesn't allow it, and the condition is not reset by initialization logic, there may be no way to reset it except by loading a new program.

If it were my system I would attack it with two EEPROM modules: buy or borrow another MicroLogix 1400 and load the program the machine should have, then send both modules. Have the end customer copy his running program into the empty module, then install the known-good-program module, then send you back the one with the faulted program. Two EPPROMs and two overnight DHL packets have to cost less than an air ticket.
 
Rohit, The mode switch will work if it is a major fault as well. It would need to be a transitory fault like a divide by zero, otherwise the fault will return instantly.
 

Similar Topics

Hi! Last few I've been trying to send message from MicroLogix 1400 to Micro 850. Unfortunately every time I failed :banghead:. Did someone tried...
Replies
6
Views
3,198
Hello, There was a mix up in information on some redeployed equipment and two of the micro 1400's that came in were hooked to 120v when they...
Replies
9
Views
1,961
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
Replies
7
Views
2,188
Does the 1100 only have 1 high speed counter, but it can have multiple inputs? And so then the 1400 has 6 HSC and you have a choice of multiple...
Replies
1
Views
1,723
Error: "Program in processor has changed causing offline state. Do you want to upload?" RSLogix500 V8.10 Micrologix 1400 Customer wants to add...
Replies
8
Views
2,292
Back
Top Bottom