Micro820 Analog Output Issue
Either have I, CCW and Micro8xx are new to me. I have this controller laying around and figured I'd try to utilize it for an upcoming project controlling a blower motor. I figured it'd be a simple deal. The drive isn't ethernet IP or Allen Bradley otherwise I'd have tried the CIP.
GOT IT....
The value should be in the 1000's for the analog to work, 10Vdc = 4000 not 4
4 is just way to low, change your scaling to match a much higher output
The output is 12 bit(Almost!) resolution so the raw value is 0-4008 so if the value of Analog-Out(0) was 2004 it would be outputting (5vdc), if the raw value was 1002(1/4 of 4008) it would be outputting 2.5vdc.
As I said before all you have to do is change your scaler MAX(Output) to 4008.
Set the output MIN to 3000 and your output min is 8vdc (approx)
Its just like setting a force in the PLC, nothing else matters
I'm probably going to just condemn this controller. I wish I had another to verify but since your code and wiring appears identical to mine I'll go with that.
If you find its bad... post it on here (plctalk), im sure there are a few people that are trying to learn and dont mind if one or two I/O's are toast, then your just not tossing PLC
I have run into a problem with my first time installing a 2080-OF2 module on a Micro820 and have a hunch that the module itself - brand new out of...
933
Hello to all. I am new to PLC’s as well as this forum so if I make any mistakes please forgive me. I am having an issue using the 2080 OF2...
2,798
Gents I'm working on a small project here and the customer requested to control the drive with 4-20mA by using Micro820 Analog output 4-20mA...
6,087
I’m trying to read values from a device that can either send registers as 32 bit or a pair of 16 bit but if I understand right, the micro can only...
26
823
Hello, I set up my Micro820 with a basic mapping. When I try to run a script to read the addresses I get errors for illegal addresses...
172