MicroLogix 1100 4-20mA to 0-10VDC issue
May 2015
Colorado
Hello,
I've hooked up (2) 1000 ohm resistors twisted together in series across the analog input on my PLC to convert the 4-20 mA signal to 0-10VDC. I've confirmed that the two resistors twisted together get close to 500 ohm, I measured with my meter.
The output on my controller to the PLC is scaled appropriately where 0 ft = 4 mA and 10.7' = 20mA.
With a level of 3.12' in the tank I would expect to get 3.12/10.7 = 29% of 10VDC or 2.9V DC. I measure 4.39 VDC and my PLC reads 444.
With a level of 5.24' in the tank I would expect to get 5.24/10.7 = 49% of 10VDC or 4.9 VDC. I physically measure 5.8VDC and the PLC reads close to that at 611.
It appears the PLC is reading accurately, but there is something wrong with the signal being converted by the resistors. Any thoughts?
Nothing wrong. I think you mean you twisted them together in parallel (2 1000 ohm resistors in parallel to get 500 ohms).
The signal is 4-20mA which means when you put 500 ohms across that you're going to get 2-10 volts, not 0-10. So when 3.12' you should be getting 4.33 volts, and with 5.24' you should get 5.9 volts, roughly. So it's close. It's just 2-10, not 0-10.
If you want accuracy you can count on use a signal conditioner.
LINK
If you are just playing around then what you are doing is fine.
If it needs to be reliable invest in the correct tools.
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
154
I am currently backing a Micro Logix 1100 and no-one seems to have the file for me to upload from. Is there a way for me to upload the project off...
556
I am trying to set up a read message in a MicroLogix1100 to read the value of a DINT in a ControlLogix5561. I have successfully set up a message...
205
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
1,205
I have a MicroLogix 1100 and it's capable of ac or dc output voltages. What I don't know is how I'm supposed to tell the 1100 to use dc for the...
1,435