NXB XIO C5:1/DN OTU C5:1/CU
Thank you Ken,
Using ADD worked. I still have a problem with the first BSL though. looks like it too needs a condition that alternates true/false.
Do you have any suggestion how to make it shift at every interrupt?
Thanks again
B3:0/13 B3:0/13
---]/[------( )---
You could instead get the CTU & BSL to trigger every scan by duplicating the rung/branch and having one triggered by an XIC of the toggle bit, the other by an XIO. This would remove the need to run it twice as often.