Micrologix 1100 losing program
rguimond
Jul 2009
Escuminac
666
Three times in the past week I have had to re-download a program onto a ML1100 installed in a rooftop A/C unit. Program seemingly evaporates...
Mircologix 1100
OS Ser B
FRN 14.0
Processor Cat no. 1763-LEC
Processor series B
Processor FRN 3.0
NO memory module
The PLC was installed to replace a proprietary circuit board assembly that came with the A/C unit in 2014. I don't recall the program evaporating until recently.
No electrical modifications. Everything is properly grounded. An Eaton powerline filter was installed when PLC was installed. Something like this: http://www.automationdirect.com/adc/Shopping/Catalog/Power_Products_(Electrical)/Power_Line_Filters/Eaton_1-Phase_Power_Line_EMI_-z-_RF_Filters_w-z-Surge_Protection/ADPV12003
One thing I did notice is that we have had a lot of lightning recently. As a matter of fact, there were over 4000 recorded discharges locally one evening last weekend and the program was lost twice over the weekend.
There were also a lot of lightning last night.
What's weird is that identical PLCs installed in similar A/C units on the same roof remain unaffected
Has anyone had similar experiences and found a solution?
If all else fails, add a memory module and set it up to load on error. You might also "set a trap" in the program so you will know if the program has been loaded from the memory module. If the unit is accessible from a remote device (HMI/SCADA) you can monitor the system bit S:5/8
I had some rooftop SLCs that had similar problems in HVAC units. Adding memory modules and setting them up was so much better than climbing on the roof with a laptop in the rain or snow to dump their brains back in every other month.
Lightning is really unpredictable. Last week, a little storm packed with static damaged about $20k in instrumentation at a water plant near my house. The radio telemetry was fine (surprisingly) but a feed pump motor blew up, and about 2/3 of the instruments on the R.O. skid got toasted. Every device and every analog channel is shielded, properly grounded and fused with 0.062 amp fuses. Most of the failed devices blew their fuses and smoked the analog channels they fed. Over the next two days, 4 more devices and analog input channels failed. We are going to keep the ticket open for a couple of weeks to make sure nothing else dies that can go on that same claim.
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
124
I am currently backing a Micro Logix 1100 and no-one seems to have the file for me to upload from. Is there a way for me to upload the project off...
532
I am trying to set up a read message in a MicroLogix1100 to read the value of a DINT in a ControlLogix5561. I have successfully set up a message...
194
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
1,194
I have a MicroLogix 1100 and it's capable of ac or dc output voltages. What I don't know is how I'm supposed to tell the 1100 to use dc for the...
1,407