Micrologix 1100 series B- Modbus RTU Master
bfranklin
Sep 2012
Alberta
125
-Channel 0 as the modbus master port
-8 slaves (Yaskawa VFD's) on a RS-485 multi-drop network
-I can talk to the slaves (Yaskawa VFD's) through MD Bus by acting as the master ( modbus testing software ) so I know the network is good and the converter.
-The 2 wire RS-485 wires go into a RS-485 to RS-232 converter then into the PLC (CH 0).
-I have the master message instruction set on a 5 second timer and have the instruction set properly with the correct slave address, and modbus holding registers
-I have changed the CH 0 comm config (ie. No handshaking, rs 485, etc)
-The message instruction comes with an error "message time out" and no values show up in the registers I assigned in the message instruction?
What am I missing?
Why are you converting to RS-232 to connect to the PLC? CH0 of the ML1100 supports RS-485 (use a 1763-NC01 and you have easy access terminals to wire directly to your 2-wire network)
Rob
I converted to RS-232 because I don't have this cable you speak of, all I have is this converter.
What exactly does this 1763-NC01 Cable do? I can't find any helpful documentation on it.
Here is the pin-out of the 1763-NC01 cable.
If you are not going to use the above cable then under protocol control/control line just use "No Handshaking without the (485 Network) with your converter.
  • 1763_NC01_cable_pin_out__Answer_ID_34450.doc
I using a HSC:0 with no problem with a encoder, but I am not able to add the second channel in order to use the HSC:1. float memory is at F8:29...
968
Hi, I have a project where I'm replacing a faulty Mitsubishi FX3s plc with a Micrologix 1100. The FX3s was using a GS2107-WTBD HMI panel. The HMI...
1,113
I have a few previous PLCs that are installed which say they are Micrologix 1100 Series A PLCs but does this mean they are 1763-L16AWA or...
1,469
Dear Forum Members, I'm new to the world of plcs and their respective programming. So I apologize for my ignorance, and thank you in advance for...
1,599
I am connecting via the Mini Din to Serial to USB, and cannot get the Mac Address to come up in BootPHP. I have previously tried with Ethernet and...
2,831