Micrologix 1400 TC module + PID + SCP
gbeaker
Sep 2012
earth
148
I have a micrologix 1400 with a 1762-IT4 module. I have channels 1 and 2 set up for "Scaled for PID" because I am using a PID to control temperature.
How do I correctly scale the units to display the temperature in degrees? If I change the data type to "engineering units" I get the correct temperature but I assume this won't work correctly with a PID.
Ok, I think I got the scaling issue figured out. Now I need some help with the PID instruction. I am not getting any output variable change, it just stays at 0. Can someone take a look at my set up and help me out?
Your Proportional Gain (Kc)) is zero!
I'd set it at 100 and then increase it in hundreds increments until the output starts oscillating; once there enter 1/2 of the value at which the output starts oscillating.
Ok, I've got it working but how to I tune it? What do you mean by the output starts oscillating? Is that when I am at setpoint?
The adjustment of the Kc is the most basic PID manual loop tuning.
Depending of the application's specific particularities, there is a value of the Kc at which, the PID output = Pv (Process Variable) will start oscillating above and bellow the Setpoint; usually this value will need to be halved and then entered as the PID Proportional Gain Kc.
Refer to http://en.wikipedia.org/wiki/PID_controller
for the PID Loop Manual Tuning theory.
Hello Friends I have a PanelView 800 (2711R-T7T) connected with a Micrologix1400 (1766-L32BWA) and an output module (1762-OW16) I have done some...
3,757
How do you program a Micrologic 1200 RTD module using a Micrologic 1400 PLC? I'm using RSLogix Micro to program the ladder logic. I've wired the...
2,844
When testing out micro, after booting the PLC without any RTDs connected, once connecting an RTD it takes up to 5 minutes before a temperature...
8,954
Getting ready to ship 38 machines we just built to one of our plants in Dominican Republic and looking at getting one of the memory module to put...
6,146
Hello Everyone, I have recently started working on a project where I have to read data using micrologix 1400 from compactlogix L35E, over the GSM...
2,054