micrologix 1763-L16bwa input power fuse

irondesk40

Member
Join Date
Jan 2008
Location
nc
Posts
630
just recieved some cutting equipment with the micrologix 1100 plc. On the 120vac power going to the plc there is a 4 amp circuit breaker. Seems like that is a little large. What size would you recommend?
 
According to the book, the 1763-L16bwa draws 52VA.

So, if the only load on the CB is the micro, then 1/2 amp would be enough, but I have commonly seen anything from 1 amp to 5 amp fuses or circuit breakers used.
 