MicroLogix Counter Question

Timk5000

Member
Join Date
Aug 2015
Location
Poplar Bluff MO
Posts
7
I am having an issue with a little Micrologix program.

Counter 1 increments each time item passes sensor on input 0
When Counter 1 increments to 5
Timer 1 starts
When Timer 1 is Done
Output 0 Turns on
Index belt advances until input 1 senses position change
Timer is Reset and everything starts over.

Problem is when the Timer 1 is reset it seems to start with a count of 1
I am not sure what I am doing wrong. In my sometimes confused mind it should work.

See Attached
 
Do you mean "counter 1" instead of "Timer 1"?

That will happen if the rung controlling the counter is still true. Try using a clear instruction with the address of the counter or a "MOV" instruction moving a value of 0 to the counters .ACC ( C5:0.ACC)
 