Micrologix issues running PID in manual mode
Aug 2017
Wyoming
I'm trying to get my PID function to go into manual mode and give the CV a value through a MOV instruction. I can set the Auto/Manual bit, and the integer value (N7:2) appears to be moving into the Control Output CV, but my control variable itself (N7:1) isn't moving.
The only way I can get my control variable to move is if I go into the PID Setup screen and manually enter the value into the Control Output CV (%) data field. See pictures for reference.
Any help would be greatly appreciated!
RSLogix PID issue logic.jpg rslogix PID issue value entered into PID setup.jpg RSLogix PID issue value entered through MOV instruction.jpg
Control Variable Percent (CVP)
CVP (Control Variable Percent) displays the control variable as a
percentage. The range is 0 to 100%.
If the PD10:0/AM bit is off (automatic mode), CVP tracks the control
variable (CV) output being calculated by the PID equation.
If the PD10:0/AM bit is on (manual mode), CVP tracks the value that can
be manipulated in the Control Variable (CV) data word.
The only way for a programmer to have control of the PID CV is to place
the PID instruction in manual mode and write to the CV word via the
control program or programming software. If no change is made to CV
while in manual mode, the CVP will display the last value calculated by
the PID equation.
Scaled Process Variable (SPV)
The SPV (Scaled Process Variable) is the analog input variable. If scaling is
enabled, the range is the minimum scaled value (MinS) to maximum
scaled value (MaxS).
If the SPV is configured to be read in engineering units, then this
parameter corresponds to the value of the process variable in engineering
units. See Analog I/O Scaling on page 303 for more information on
scaling.
Output Parameter
Descriptions
Address Data
Format
Range Type User Program
You need to write to the CV while in manual.In your case N7:1 (0-16383) (see excert from manual above)
So I got my ML1100 up and running last night, and tonight Im trying to connect an analog in/out module 1762-IF2OF2. The problem is that the green...
2,250
Hi everyone. I'm having major issues with both channels on my micro, all of which are self inflicted. Firstly I've been having trouble settling...
1,724
A customer of mine has a ML 1500 LRP connected to a Net-AIC+ via the mini din connector (CH 0 of plc to port 2 of AIC) from this AIC then connects...
1,784
Dear all, I am commissioning an untested system of HMI: Mitsubishi GOT Simple GS2107 PLC: Micrologix 1400 B, 1766-L32BWAA Cable RS232...
4,642
Hi guys I have an micrologix 1400 on Ethernet what keeps getting a coms error where the hmi gets stars in the data boxes ? This is an...
1,346