I currently have a Micrologix system but feel I need to prevent one output from failing and turning ON a motor starter. The system has an E-Stop Safety Relay on it but feel it would be too late to prevent an injury. I know there are safety PLCs out there and even programmed the AB SmartGuard 600. What can I do with the existing Micrologix?
What do you guys feel about something like the attached... It shows the Micro Output wired in series with a Force guided relay that is controled by a start button and is latched in.
Could make it two start buttons... What about driving some kind of Safety Relay? Two Micro Outputs driving a two channel Safety Relay...
What do you guys feel about something like the attached... It shows the Micro Output wired in series with a Force guided relay that is controled by a start button and is latched in.
Could make it two start buttons... What about driving some kind of Safety Relay? Two Micro Outputs driving a two channel Safety Relay...