I need make hard wire for MM420 (Manual function for control panel) MM420 must have input and output for into drive control by not via PLC because it's safety function of the industial.
Thank you for your help.
Thank you for your reply.
I know connection . but don't know how to use DI and other such as DI has 3 bit and ,So bit 0 set is 1 for what? , and bit 2,3 ......i want to detail about DI,DO,AI,AO
please Reply me again, Thank you for information....
Hello ahmadd;
Sorry, but there is no esay and fast answer to your questions.
Here is a link to all documents available on the Micromaster 420 on Siemens' website:
http://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&siteid=cseus&objid=10869802
All drives have analog and digital iputs/outputs. What you do with them depends on the way you set up the parameters of the drive.
Example:
Dig 1 could be the "Run CW" signal and Dig 2 could be the "Run CCW" signal, if yiou set the following parameters this way:
P0700=2
P0701=1
p0702=2
In the above link, look at the manuals, parameter list and FAQs for more information.
Hope this helps,
Daniel Chartier
hi
1)connect digital input(24dc+) to DIN1 ie terminal 5
2)connect port reference(signal)to AIN+ ie terminal 3
3)connect 0 v to AIN- ie terminal 4
4)connect 0 v to terminal 9
5)In parameter 700 select 2
6)In parameter 1000 select 2
7)In parameter 701 select 1
8)In parameter 719 select 2
This will do the job.
Manmeet
Sawatdee T.Ahmadd.
Using only the command signals on the terminal strip is normally NOT recommended for safety functions. There are VFDs with onboard safety stop via the terminal strip, but an MM420 is not one of them.
Put a contactor in FRONT of the VFD. Let the contactor be constantly on, except when there is safety stop. This is simple, reliable, and does not cost very much.
I do like this and have a profibus connection to the VFD for the normal control.
Evening all. Got a bit of a problem here, process was running fine, 440 fails, new one installed, process not running fine anymore! I've never...
4,386
Hello Everybody, Recently we changed the gearbox which has different ratio than the original one on a motor which is controlled by Micromaster...
1,901
Hello Experts I have to to make a backup of Siemens micromaster mm 440 with RS 485 to terminal 29&30. I use starter or drive monitor Do i need...
1,209
:utoh: Hello, today tryed houres to connecting the micromaster 420 of my kaeser compressor to my laptop with the connection kit (MM4...
1,726
My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
2,977