Hello Everybody,
Recently we changed the gearbox which has different ratio than the original one on a motor which is controlled by Micromaster 420 vfd . Now I see the speed is not upto required speed.
Is there any way to make changes to parameter list on drive to match the speed as before with this new gearbox ?
Thanks in advance!
Yes, it would be the commanded speed
Not sure how your commanded speed is in either 3 places typical. Read manual!
it can be done by either hardwired input speed control.
Pot dial on front if in local control
If some type of networked speed control. Go to that word to change speed
Need a Tach to read the speed on your unit.
You can calculate the new speed by a cross multiple
old Hz new Hz
TachSpeed RPM Speed I need RPM
for some reason formatting above is sketchy
Cross multiply and divide above get your new Hz
It will depend on how you control the drive & the difference in the gearboxes, for example: let's assume the speed is normally controlled from either an analogue from the PLC or a potentiometer, then if the gear ratio is not that greater difference then just increase the max Hz on the VFD for example if it is say 50Hz then increase the range to perhaps 65Hz bear in mind that there is a limit that the motor will run at a higher frequency than it's rated.
I have seen drives perform well even at 80Hz, the analogue signal i.e. 0-10v will give out a frequency of 0-max of the settings so for example if the min speed is 0 & the max speed is 60Hz then the 0-10v will equate to 0-60Hz, by increasing the max Hz setting to say 70Hz will give a range of 0-70Hz on the 0-10v.
C
i m connecting a servo motor to a gear box with direct coubling method. This gear box is in ratio 1 to 5. Does this ratio will affecting the value...
14,119
Has someone tried MC_TorqueLimiting along with MC_GearIn , on a Siemens S120 axis , controlled by an S7-1500T plc ? If we limit the torque ...
1,597
Hello, Does anyone know the preset thermal limits for SEW Movigear SNI B drives. Randomly experience overtemperatures of the heatsink of the...
719
Gents, We have several machines where we use 1 till 25 baseplates to make products. Depending on the type of product, we use more or less...
1,410
Hi everyone. I have a micrologix 1400 HSC reading a prox on a 40PPR large diameter (12") gear. This gear has large trapezoidal teeth. 500 RPM max...
41
12,485