Gents,
We have several machines where we use 1 till 25 baseplates to make products.
Depending on the type of product, we use more or less baseplates.
Every baseplate has 4 SEW Movigear motors with the CBS51A safety option.
Our PLC is a Beckhoff TwinCAT with TwinSAFE, and so we use Safety over EtherCAT.
The problem is now that we never know which baseplate will be connected where on the machine, and so we don't have a fixed configuration in the SafetyPLC.
The Safety FSoE addresses in TwinSAFE need to be the same as at the connected motors. But as explained before, we don't know which motors will be connected on forehand.
I've try to work around this issue!
I've tried to write the FSoE address of the motor with a startup list parameter, but this isn't accepted by the motor.
So the question is:
is there a way to read the motor FSoE address at the moment when we connect this motor, and write this address in the TwinSAFE project?
Thanks in advance!
Jack
Gents,
I've made some progress today while I was at SEW in Rotterdam with my configuration with the 2 test motors. Together with an engineer of SEW we found out that it is possible to use the same FSoE and BusCrc address for each of the motors.
It's needed to set the Safe Addres Verification of the Target System to "Allow multiple usage".
The only problem which is left, is that we not always use the full configuration of motors which are configured as Alias Devices in the TwinSafeGroup.
The guestion is: is there a way to disable not connected Alias Devices in the TwinSafeGroup?
Thanks in advance!
Jack
Use the inhibit checkbox if not using that motor on your io config tree. Maybe there is a tag associated with the inhibit checkbox that could be used to disable code that is looking at that motor?
Gents, I've a Beckhoff TwinSAFE project in TwinCAT 3 where I've 2 EL6910 Safety controllers, and need to exchange data between them. So I...
831
Hello everyone, I'm new here :) Has anyone worked on beckhoff twinsafe el6900 programming. I have a twinsafe program in the plc with emergency...
1,636
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
199
Hi , I am trying to replace an old inverter with a new one and its giving me issues . Once the new one was installed , the S7-300 PLC started...
127
Hello Everyone. Looking to see if any of you have encountered an issue with these drives. We have a major installation with around 30 of these...
94