Migrating from a 1336 to a Powerflex 700 on a PLC 5/60
DCom
May 2016
Conroe
20
I currently have a PLC 5/60 controlling a 1336 drive on remote i/ o and need to convert to a Powerflex 700. I have been told by a couple of people that all I have to do with the logic is just move down one word on the inputs and outputs. I haven't actually ever been involved on this type of migration. Any help would be appreciated. Thanks
You may need to adjust your logical racks and also depending on what data is being pass the powerflex series is 32 bit and the PLC 5 is 16 bit so you may have to do some works to convert these issues.Using the 20-Comm-RIO cards the data is in multiples of 1000 so your 30 HZ reference or feedback will be 30,000 for example.
The best way I have found to do it is with this http://www.prosoft-technology.com/P...-IP-to-Allen-Bradley-Remote-I-O-or-DH-Gateway
Is there any manual or website I could refer to on the issues with converting. Since the PLC 5 is 16 bit, I assume that I will need to use two words for input and output for controlling the 32 bit drive?
Another thing to consider is that by using a 20-COMM-R and using datalinks, you will need to use Block Transfer instead of IO addressing that the 1336 uses.
From memory the 20-COMM-R manual shows some programming examples.
Alan
I've got a machine in my mill running on PLC5 with 7 different 1336F drives over Controlnet. I've been tasked with migrating these to Powerflex...
3,709
Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
50
We are upgrading our FTV ME v8.1 program to SE v12. Is there any way to migrate the alarm tags (about 600ish) from ME to SE. The import / export...
846
Can it easily be done ? We have a legacy project written on Allen Bradly 1746-l542 with Several racks of some on an extension rack and some on A...
1,751
I just want to get others thoughts on what is the biggest obstacle one faces in migrating to a newer system? For me with the few systems I have...
17
4,128