Mitsubishi E700 vfd parameter
Apr 2019
Karachi
23
Hey Every one
I am trying to set to frequency of vfd to 100z but cant
the parameter #125 is the parameter to set the frequency of vfd more than 70 hz but vfd not showing the pr#125
I dont know which parameter is disable
Which parameter i need to enable for change in frequency of vfd
PLease help
Thanks alot bro it's working through external terminals
I want to control it through keypad.
I also want to know how i can unlock parameter 125
Regards
When you say it's set through external terminals do you mean the low med & high terminals i.e. RH RM RL then the speed is controlled by the parameters PR4 -6 or do you mean use keypad to increase or decrease the speed. Parameter 125 seems to be for PID control so I don't think this is what you need to change
Yeah you right bro
Yeah bro i want to run the vfd through keypad.
When i run the vfd through keypad it's run at 60 hz maximum but when i run the vfd through external terminal the vfd run at the frequency set in parameter 38.
It might be password protected. Par. 296 shows what level of parameters are locked, 297 is where you put in the unlock code. If you don't know the code, you might be out of luck.
The default is 9999, but if someone changed it, you only get 3 - 5 attempts (programmable number) to guess before it trips the drive and you are locked out of resetting it. So be careful. If this was built by an OEM, I would call and see if they will give you the code first. Mitsi might have a back-door code, but that's not guaranteed.
Hello Everyone I am trying to establish RS485 communication between Mitsubishi vfd E700 and delta plc DVP20EX00R2 The problem i am facing...
2,474
Hi every one!! I successfully communicate the delta plc with Mitsubishi e700 vfd/ The problem is that i want to give run command to vfd through...
4,297
Hi all, I'm hoping someone can help me with obtaining firmware files for a Beijer E700 HMI terminal. I'm looking for v4 firmware. I have an HMI...
2,780
I am going to replace the above HMI.Do I need to reprogramme or just plug in ,power on and auto-load from the PLC and run like the Siemens S6 do ...
4,250
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
47