there is an old mitsubishi Q2AS cpu, i want to take data from it to the mx ops server.

Can I connect via rs422 directly to the cpu module via rs422 to usb converter at a distance of 100 meters or do I need to install some special communication module for such a distance?

1.PNG
 
422 can do it upto 1,200 metres at 10mb/s so there should be no problem however, never tried it on a USB to 422 converter at that distance. I have run USB/232 at 70 metres at at a baud rate of 9600 some USB/232 (perhaps 422) may vary on their ability had one that kept dropping off another was fine.
The A2 series are now not supported I believe so getting cards i.e. ethernet etc. may be difficult, does MX still support the A series.
I do know the A2 is only supported in GXDeveloper not GXWorks 2
 
422 can do it upto 1,200 metres at 10mb/s so there should be no problem however, never tried it on a USB to 422 converter at that distance. I have run USB/232 at 70 metres at at a baud rate of 9600 some USB/232 (perhaps 422) may vary on their ability had one that kept dropping off another was fine.
The A2 series are now not supported I believe so getting cards i.e. ethernet etc. may be difficult, does MX still support the A series.
I do know the A2 is only supported in GXDeveloper not GXWorks 2


it is very interesting. as far as I know, for rs232 the maximum line length cannot exceed 15 meters and for rs422 length 1200 metes only at 10kbit/s

but my question concerns a specific processor, is it designed to work through the port built into the cpu?
 
I have never tried MX coms on a A2, however, I do know that the Beijers HMI (re-badged by Mitsubishi) could access data from the programming port & I believe that Kepserver can also so I assume it either uses the programming protocol or perhaps the MC protocol, Not worked on A2's for many years but I have connected FX2N/3U & Q series I have used a tcp/422 converter to get data using Kepware I have also connected the Beijers HMI's to them as the A series is now redundant the only thing I can suggest is perhaps get a trial copy of Kepware KepserverEx & try that on a USB to 422 converter My copy of Kepserver is about 5 years old so not sure if they still support it in later versions.
The trial version allows you to connect for 10 minutes at a time a re-start will give you another 10 mins as many times as you like.
I do not have MX Component or server but used the component in the past
I think you need to check that the newer MX OPC server still supports the A series.
Edit: Just looked at the MX opc manual & it does say it supports A2 series standard serial interface but only at 9600 baud via programming port so using perhaps either MX or a copy of Kepserver
& an SC09 cable to a USB/232 converter local to the PLC to start with will give you some idea if it will work, I suggest the SC09 as I know this works from win 11 if you have a converter with the latest FTDI chipset.
 

Similar Topics

Hi guys, I'm trying to read the program from Mitsubishi Q2AS(H) PLC. The communication is fine. But while uploading program, selection for...
Replies
3
Views
4,244
Hi all, I use a Q2AS-S1 CPU, with a Q1MEM-512SE SRAM+EEPROM memory module. I want to save some file registers on the EEPROM. To do so I use the...
Replies
0
Views
2,414
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
Replies
0
Views
59
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
Replies
0
Views
56
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
Replies
0
Views
64
Back
Top Bottom