I have added an extention block to my Mitsubishi FXon 24mr-es it is a 40er-es.
It has 3 lines of inputs 0-7
and 2 lines of outputs 0-7
How would I write these i/o's in GX Developer and do I have to tell the software there is an extention present?

Thanks
Norman
 
I cannot remember the I/O configuration of the 24mr - so I will presume it is 12 in 12 out. (but maybe 16 in 8 out)

But it doesnt really matter as the inputs and outputs follow on from what you have on the main unit.

ie X0 - x7 X10 - X13 In this case your first input will be X14 and the same with the outputs, they just follow on.

You do not have to configure the extra I/O in the software.
 
let us begin give the PLC

let us begin give the PLC I to seek the configuration of PLC series fx of mitusubishi
 

Similar Topics

Hi I am using Simatic field PG M4 with its original RAM (4GB 2RX8). I wish to increase its RAM using addition RAM and ordered one unit...
Replies
4
Views
1,466
We are using 6ES5734-1BD20 TTY/RS232 converter cable for communication between S5-115U and OP77 Panel.This converter cable max.length is 3.2m and...
Replies
3
Views
5,452
Hi, I have OMRON PLC type CPU C500HS. At the moment for troubleshooting I need more time to solve it because the location of the CPU unit inside...
Replies
0
Views
2,601
Hello I have a question about communication plc with profibus. what tools we have need if we want to have 2 nodes (slaves) with cpu315-2Dp...
Replies
4
Views
1,886
I was wondering how can I read a .RSS extention. What program do I need to read it? I the any particular way I should save it? thanks
Replies
12
Views
2,895
Back
Top Bottom