modbus and DL205 (250-1 CPU)

Have you called AutomationDirect Tech support? 800-633-0405You can access them till 6:00 PM Eastern

Andy
 
Ok, so far there are several things that have been said that are incorrect so far.

1. Port 1 can be a MODBUS slave. It is set for 9600 baud, odd parity, and 1 stop bit.

2. You only need pins 4 & 5 jumpered for RS-232 on Port 2. Do not jumper any others. Pins 7 & 8 are the same potential, ground. You say your cable is right, did you swap pins 2 & 3 (RXD-TXD & TXD-RXD) or do they go through straight (RXD-RXD & TXD-TXD)?

3. Make sure your baud, parity, and stop bits are configured the same in your master device as in the PLC Port 2 setup.


If you are really struggling with this call AD's tech support, they can get you going probably in a few minutes (800-633-0405).
 
2. You only need pins 4 & 5 jumpered for RS-232 on Port 2. Do not jumper any others. Pins 7 & 8 are the same potential, ground. You say your cable is right, did you swap pins 2 & 3 (RXD-TXD & TXD-RXD) or do they go through straight (RXD-RXD & TXD-TXD)?

Actually he said that someone told him that pins 7 & 8 need to be jumpered on the PC side, which is RTS to CTS. I suppose this is possible. It depends upon the way that software was written (does it looks for CTS before it TXs?).

Question: Is the final software you plan to use or are you simply trying to validate your Modbus setup? If you are just trying to validate the Modbus setup, I would suggest a different software. The software that you are using seems very confusing to me. Both www.win-tech.com and www.modbustools.com have very good simulator softwares that have freel trial versions you can download.
Calling tech support is probably a good idea but my guess is they will want you to try one of these other simulators.
 
Thanks guys. I got it figured out, sort of. A tip from another with a DL06 recommended changing my parity from ODD to NONE, and changing the Base Timeout setting in DS32 to Timeout X 1.5. All of a sudden it 'magically' worked.

I plan to go back and change settings one at a time to see which one did the trick.

I appreciate all the tips, it was just one of those things that I got hung up on.
 

Similar Topics

I am trying to connect a DL205 PLC to an equipment monitoring network to record when the machine is in cycle. I have an H2-ECOM100 connected to a...
Replies
1
Views
1,620
Hello- what is the best way to interlock the VFD if i lose the communication link? if the drive is running and i pull the comm connection it...
Replies
2
Views
1,612
O boy- my pea brain is taxed right now... here's the issue i have a chiller that will only communicate when the parity is set to none and the stop...
Replies
9
Views
1,997
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
11
Views
227
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
5
Views
168
Back
Top Bottom