DL205 Modbus and GS-2?
dginbuffalo
Dec 2010
Buffalo,NY
630
Hello- what is the best way to interlock the VFD if i lose the communication link? if the drive is running and i pull the comm connection it continues to run. Is my only option running an output to the VFD's ext fault input? Seems like a waste if your trying to do everything across Modbus. o_O
While we don't use the GS2 our method is to perform start/stop with a hard contact. Issuing of speed and reading of status is done through Modbus. We set the drive to 'Continue last' (Powerflex 4) but we monitor any fault in the status or any communication error and shut down the 'start' output.
Parameter P9.03 in the GS2 seems to set the response to a communication fault.
I am trying to connect a DL205 PLC to an equipment monitoring network to record when the machine is in cycle. I have an H2-ECOM100 connected to a...
1,623
O boy- my pea brain is taxed right now... here's the issue i have a chiller that will only communicate when the parity is set to none and the stop...
1,998
Hello, I've got some CNC control software (G-Code interpreter, etc) used for retrofitting lathes, mills etc... It has the capability to be a...
18
9,490
Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
66
I have some AD Direct Logic 205 series processors, racks and I/O cards, etc. that I used for development previously. It's (almost) useless to me...
4,544