74
In one application, the user wants to connect their DCS with Modbus RTU on RS485 to SLC 5/03. I think SLC5/03 natively supports only DF1 or DH485. What will be the cheaper and more reliable solution in this case - using a DH485/Modbus gateway or using the Prosoft MVI46-MCM Module? or are there any other options?
SVN
ProSoft’s 3150-MCM module, able to directly connect Allen-Bradley’s SLC for modbus communication will be best option
Thanks rPraveenkum,
I downloaded the 3100 3150 User Manual also. I shall go through the manual but mean time can you just tell me the major differences between this module and MVI46-MCM?
SVN
Thanks rPraveenkum for the link
BTW has anybody used DL3500 DH485/Modbus Link? How is it?
SVN
rPraveenkum said:
DL3500 is a DH+ to Modbus protocol Convertor
But in the DL3500-dh-385-modbus Application Note , DataLink have mentioned that it can be used for DH485 also if DH485 Commands in PLC5 format are used with SLCs, Micrologix etc. Does SLC5/03 not support these commands?
SVN
We have a SLC5/05 that's acting as the main MTU for our SCADA system. I need to bring in some data from an AutomationDirect CLICK PLC that...
3,456
After viewing the posts of others and helping whenever I could, it's time for me to post a topic and get some free advice. But then again, you get...
8,521
Hello Everyone, I am using a raC_Opr_NetModbusTCPClient AOI module, as below,. So, I need some assistance to restrict in reducing the poling...
91
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
68
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
327