I'm hoping to use an SLC 5/05 PLC to communicate as Modbus RTU Master to a number of Modbus TCP slaves. I understand that a gateway is required to switch protocols however the budget for the project is fairly limited as it is a college project.
My question is whether the SLC 5/05 would be able to implement Modbus RTU over the DF1 RS232 port, or would one of the Prosoft Modbus modules be required.
Also, assuming this would be possible, what type of gateway would be required. There seem to be a number of RTU to TCP gateways around but they're all RS485 to TCP and since the PLC only has an RS232 port i'm unsure how to proceed.
Thanks in advance.
Thanks in advance.
I would have imagined the easiest way to do this would be to add a Modbus TCP card to the PLC if such a thing i available (i don't used SLC)
A Schneider EGX150 will do Modbus RTU with RS232 on master side Modbus TCP on the slave side
https://www.schneider-electric.com/...t-gateway---2-ethernetport---24-v-dc-and-poe/
Or an Anybus may have something that will work
Hi and welcome to the Forum fellow Paddy!
mcmahobr said:
...My question is whether the SLC 5/05 would be able to implement Modbus RTU over the DF1 RS232 port...
If you can read the following Rockwell Automation Knowledgebase technote article: -
58253 - SLC Processors that Support Modbus Protocol
Access Level: Everyone
There you will see that support for Modbus RTU Master capabilities on the SLC modular controllers, including the 5/05, using the Channel 0 RS-232 serial port, was added at firmware revision "OS 501 Series C FRN 11", which was released about 10 years ago.
You must also be using RSLogix 500 v8.1 or later to support the selection of Modbus RTU Master for the Channel 0 serial port.
Do you have the controller or know what firmware series and revision it's currently at?
The latest is "OS501 Series C FRN 13" (released 2016) and if you need it then you can download it from here...
FIND DOWNLOADS
Type "SLC 5/05" in the search field.
Any further question fire away.
Regards,
George
Its a series C 5/05 with the frn 7 firmware, i got the download for the latest firmware but haven't gotten around to flashing it yet. I can configure the Rs232 port for Modbus in RsLogix too so i'd say that's fine.
Knowing that'll work fine with the RS232 port will certainly save a lot of heartache as far as my budget is concerned anyway. I've had a look since for specifically Rs232 to TCP gateways and there's plenty of affordable options on ebay.
Thanks for the replies, that's cleared a lot up!
Regards,
Brian.
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
236
Hi friends, this is my first post in this forum. I am Implementing an application that works like this: I want use the RS-485 interface of...
4,728
we are trying to do a Modbus Rtu communication between a Delta plc and an Abb inverter, using ISPsoft and NWconfig. do you have any sample program...
3,939
I am trying to communicate from a Micrologix 1400 chan 2 to a SC2124M scanner via modbus rtu. I have taken a straight through cable with RS232 on...
2,791
Hi, I have a project using a panel view plus 1000 communicating using kepware over Modbus RTU serial. Initially I was getting a com1 OS 12 error...
2,470