Modicon M340 Modbus TCP and Modbus Serial?
Feb 2008
Walnuc Creek, CA
31
I'm looking to purchase an M340, and need it to communicate over Modbus TCP to several devices and Modbus serial to a few others.
First off, this seems like standard operating procedure, but I wanted to verify that this is in fact possible before making the time/money investment.
Secondly, when doing this, from a programming standpoint does it look as if it's all one Modbus network? For instance, would I use the DATA_EXCHG function block to issue commands over both, the only difference being that I reference the devices independently by their Modbus ID?
Thanks in advance for your help.
Yes it is possible
For both ModbusTCP and Modbus serial (assuming the M340 is to be the master) you would use the Read_Var and Write_Var functions. The Addm function is used to generate the address.
This is all available on the built in ports on the higher level M340, however I would look at using a NOE module for the ModbusTCP. The NOE module will give you access to a lot more functionality (DHCP server, IO scanner - just fill out a table to setup all your comms, Global data, Messaging, Email notification, FDR - faulty device replacement)
hope this helps
Geoff
Hello, For my project I have to read and write coils/registers of Scheider Modicon M340 PLC. To do so, I decided to use a python script based on...
4,856
I have a PLC rack with an M340 processor (BMXP342020). Using Unity Pro 7. My task is to interface to a Modbus plus network. Do you know of any...
2,128
Hello, I am currently working on a project on Modbus TCP communication between a Modicon M340 PLC and an electronic card with a DSP Texas...
20,256
Hi, We need to setup Modbus TCP/IP communication between "BMX NOE 0110" (Modicon M340 module) and "IC695ETM001" (GE PAC RX3i module). Manuals say...
5,952
Hi, I am trying to communicate modicon M340 PLC with an Schneider T200 Remote main unit controller over modbus TCP. the PLC has got in built...
5,165