Modicon TSX Quantum- AVI030-00 8 Channel Analog Input

Ones_Zeros

Member
Join Date
Feb 2014
Location
at work
Posts
367
Hello
I was needing help with the proper scaling on a Modicon TSX Quantum- AVI030-00 8 Channel Analog Input PLC card.

What would be the proper RAW scaling on the 4-20mA signal on the card.
I'm having an issue with getting the value scaled properly.

I have tried 0-4095, but doesn't get the scaled value correct.
When i use 0-64000 it gets the scaled value correct, but the value runs off after a few days.

I have the Eng scaling 0-20

Here is some pics of the scaling blocks

Moisture-PLC-Scaling-RAW-Analog-Data.jpg


Moisture-PLC-Scaling.jpg


I appreciate the help
 
Check how the channel on the card is configured. Make sure it is 4-20mA. If the channel is set to 12 bit resolution 0-4095. If set to 16 bit resolution 6400-32000.
 

Similar Topics

Where I can find Linear Measuring Ranges Table for Modicon TSX Quantum 140ACI03000 module?
Replies
5
Views
6,424
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
45
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
136
Pure mind boggled at this one, can’t seem to figure it out. NO contact with - %M130(%MW11) How is this possible? Is the %MW11 0 it’s logic 0, 1...
Replies
5
Views
1,537
Hi All, i have PLC Modicon TSX 3722 Micro i need to know where should i put the socket of programming cable on Ter or Aux port. and i see the file...
Replies
0
Views
1,636
Back
Top Bottom