Module Defined Data Type in RSLogix 5000
recondaddy
Apr 2006
Atlanta, GA
77
Hello,
This is not a question that's causing me problems, but I'm uncomfortable not understanding it:
In RSLogix 5000, I have a module-defined data type for an Ethernet/IP commanded stepper. When I open the MDDT, Logix tells me that it is 20 bytes. However, I'm seeing 24 bytes in the member list. What gives?
Here's the structure
Code:
COMMAND_WORD_0, INT, Binary
Bit_1, BOOL, Decimal
Bit_16, BOOL, Decimal
COMMAND_WORD_1, INT, Binary
Bit_17, BOOL, Decimal
Bit_32, BOOL, Decimal
POSITION, DINT, Decimal
SPEED, DINT, Decimal
ACCEL, INT, Decimal
DECEL, INT, Decimal
CURRENT, INT, Decimal
JERK, INT, Decimal
If you add up all the INTs, BOOLs, and DINTs, you come up with 24 bytes. If you exclude the BOOLs, you get 20 bytes.
Now, looking at the manual, I see that the BOOLs actually correspond to the individual bits of the COMMAND_WORDs that precede them, and obviously RSLogix recognizes this.
My question is, why isn't RSLogix counting those BOOLs? Does it have to do with something in the EDS file? When I try to replicate this structure with a UDT, the BOOLs get counted.
Thanks.
I only count 20 bytes in your list:
2 bytes COMMAND_WORD_0
2 bytes COMMAND_WORD_1
4 bytes POSITION, DINT
4 bytes SPEED, DINT
2 bytes ACCEL, INT
2 bytes DECEL, INT
2 bytes CURRENT, INT
2 bytes JERK, INT
The BOOLS are overlays of the Command Word 0 and Command Word 1 integers, so they do not get their own memory space.
Am I just adding incorrectly ? I've had only one cup of coffee this morning.
The following Rockwell Technote discusses UDT memory allocation:
RSLogix 5000 User Defined data types (UDT) (TechConnect Required)
In it, there is reference to members "hidden from the user" in the situation where boolean elements are encapsulated by a larger integer (i.e., SINT, INT, or DINT). It may be possible this is what is happening with the COMMAND_WORD_ integers in this module defined type.
This is a just a guess, but if examined in the L5K file it might appear as implied by the technote:
data type xxx_UDT (FamilyType := NoFamily)
INT COMMAND_WORD_0 (Hidden := 1);
BIT Bit_1 : 0;
BIT Bit_2 : 1;
BIT Bit_16 : 15;
INT COMMAND_WORD_1 (Hidden := 1);
BIT Bit_17 : 0;
END_DATATYPE
I'd be curious if this is what you find.
This is a just a guess, but if examined in the L5K file it might appear as implied by the technote.
The L5K only contains user defined types in this format, not module defined types.
For what it's worth, I did find the attached UDT yields the following datatype in the L5K:
DATATYPE udt_Bools (FamilyType := NoFamily)
SINT ZZZZZZZZZZudt_Bools0 (Hidden := 1);
BIT b1 ZZZZZZZZZZudt_Bools0 : 0;
BIT b2 ZZZZZZZZZZudt_Bools0 : 1;
BIT b3 ZZZZZZZZZZudt_Bools0 : 2;
BIT b4 ZZZZZZZZZZudt_Bools0 : 3;
BIT b5 ZZZZZZZZZZudt_Bools0 : 4;
BIT b6 ZZZZZZZZZZudt_Bools0 : 5;
BIT b7 ZZZZZZZZZZudt_Bools0 : 6;
BIT b8 ZZZZZZZZZZudt_Bools0 : 7;
END_DATATYPE
4 bytes SPEED, DINT
2 bytes ACCEL, INT
2 bytes DECEL, INT
2 bytes JERK, INT
Ken, that is absolutely correct. The BOOLs are, as you say, overlays of the Command Words. My question was concerning how RSLogix recognized them as such and didn't assign them their own memory space.
I guess what I'm really trying to find out is whether this is a capability that we have in UDT creation, or is it something that can only be done with Module-Defined Data Types.
As I said, when I tried to replicate this exact structure in a UDT, it calculated 24 bytes, since it assigned the BOOLs to their own memory space.
Thanks.
Ken gave me the terminology that I was looking for to do a meaningful search.
From the Knowledgebase:
Question
Are bit overlays supported in RSLogix5000?
Answer
Bit overlays are not currently supported by the RSLogix 5000 software Data Type Editor.
Users can edit the .L5K file externally from RSLogix 5000 software and create structures that uses bit overlays. While this is possible to do this, the RSLogix 5000 Data Type Editor will not support the modification of such structures, and therefore the view will be read-only.
[UDT Example]
data type MyBits (FamilyType := NoFamily)
SINT ZZZZZZZZZZMyBits0 (Hidden := 1);
BIT MyBit0 ZZZZZZZZZZMyBits0 : 0 (Radix := Binary);
BIT MyBit1 ZZZZZZZZZZMyBits0 : 1 (Radix := Binary);
END_DATATYPE
Need to remove the (Hidden := 1) reference.
Need to rename the ZZZZZZZZZZ references.
[Bit Overlay UDT Example]
SINT MyOverlay;
BIT MyBit0 MyOverlay : 0 (Radix := Binary);
BIT MyBit1 MyOverlay : 1 (Radix := Binary);
END_DATATYPE
Once Imported back into RSLogix 5000 software, the user can no longer edit this structure.
When they create a tag of this type, they will notice the Bool members represent each bit in the SINT structure.
This allows each Bool bit to have an individual name.
Using the template from the Tech Note, I was able to create my own data type in the L5K file with bit overlays:
Code:
DATATYPE SMD23E2_Status (FamilyType := NoFamily)
	SINT SMD23E2_Status0 (Hidden := 1);
	BIT ConnectionFaulted SMD23E2_Status0 : 0 (Radix := Binary);
	INT STATUS_WORD_0 (Radix := Binary);
	BIT Moving_CW STATUS_WORD_0 : 0 (Radix := Binary);
	BIT Moving_CCW STATUS_WORD_0 : 1 (Radix := Binary);
	BIT In_Hold_State STATUS_WORD_0 : 2 (Radix := Binary);
	BIT Stopped STATUS_WORD_0 : 3 (Radix := Binary);
	BIT At_Home STATUS_WORD_0 : 4 (Radix := Binary);
	BIT Accelerating STATUS_WORD_0 : 5 (Radix := Binary);
	BIT Decelerating STATUS_WORD_0 : 6 (Radix := Binary);
	BIT Move_Complete STATUS_WORD_0 : 7 (Radix := Binary);
	BIT In_Assembled_Mode STATUS_WORD_0 : 8 (Radix := Binary);
	BIT Wait_For_Assembled_Segment STATUS_WORD_0 : 9 (Radix := Binary);
	BIT Position_Invalid STATUS_WORD_0 : 10 (Radix := Binary);
	BIT Input_Error STATUS_WORD_0 : 11 (Radix := Binary);
	BIT Command_Error STATUS_WORD_0 : 12 (Radix := Binary);
	BIT Configuration_Error STATUS_WORD_0 : 13 (Radix := Binary);
	BIT Module_OK STATUS_WORD_0 : 14 (Radix := Binary);
	BIT Mode_Flag STATUS_WORD_0 : 15 (Radix := Binary);
	INT STATUS_WORD_1 (Radix := Binary);
	BIT IN1_active STATUS_WORD_1 : 0 (Radix := Binary);
	BIT IN2_active STATUS_WORD_1 : 1 (Radix := Binary);
	BIT Temperature_Above_90C STATUS_WORD_1 : 2 (Radix := Binary);
	BIT PLC_in_PROG_Mode STATUS_WORD_1 : 3 (Radix := Binary);
	BIT Connection_Was_Lost STATUS_WORD_1 : 4 (Radix := Binary);
	BIT Driver_Fault STATUS_WORD_1 : 5 (Radix := Binary);
	BIT Invalid_Jog_Change STATUS_WORD_1 : 6 (Radix := Binary);
	BIT Limit_Condition STATUS_WORD_1 : 7 (Radix := Binary);
	BIT Heartbeat_Bit STATUS_WORD_1 : 8 (Radix := Binary);
	BIT Multi_turn_Encoder_Error STATUS_WORD_1 : 9 (Radix := Binary);
	BIT Acknowledge_Flag STATUS_WORD_1 : 10 (Radix := Binary);
	BIT Stall_Detected STATUS_WORD_1 : 11 (Radix := Binary);
	BIT Drive_Is_Enabled STATUS_WORD_1 : 12 (Radix := Binary);
	DINT MOTOR_POSITION;
	DINT ENCODER_POSITION;
	DINT TRAPPED_ENCODER_POSITION;
	INT PROGRAMMED_MOTOR_CURRENT;
	INT JERK_STATUS;
END_DATATYPE
If you want to know the exact size and layout of a module-defined datatype, open, close and reopen your ACD file in RSLogix 5000, then search in the Windows user's TEMP folder for an XML file named TagInfo. This file is temporary, so don't close RSLogix yet. If you are familiar with the L5X file format, the contents of this file will be easy to understand and will take the guesswork out of figuring out where the padding bytes and unused bits are. You could use this information to verify that your UDT was created correctly.
There, I fixed it. Corrections in bold.
Code:
	[B]DINT[/B] SMD23E2_Status0 (Hidden := 1);
	BIT ConnectionFaulted SMD23E2_Status0 : [B]1[/B] (Radix := Binary);
	BIT Temperature_Above_90C STATUS_WORD_1 : [B]4[/B] (Radix := Binary);
	BIT PLC_in_PROG_Mode STATUS_WORD_1 : [B]5[/B] (Radix := Binary);
	BIT Connection_Was_Lost STATUS_WORD_1 : [B]6[/B] (Radix := Binary);
	BIT Driver_Fault STATUS_WORD_1 : [B]7[/B] (Radix := Binary);
	BIT Invalid_Jog_Change STATUS_WORD_1 : [B]9[/B] (Radix := Binary);
	BIT Limit_Condition STATUS_WORD_1 : [B]10[/B] (Radix := Binary);
	BIT Heartbeat_Bit STATUS_WORD_1 : [B]11[/B] (Radix := Binary);
	BIT Multi_turn_Encoder_Error STATUS_WORD_1 : [B]12[/B] (Radix := Binary);
	BIT Acknowledge_Flag STATUS_WORD_1 : [B]13[/B] (Radix := Binary);
	BIT Stall_Detected STATUS_WORD_1 : [B]14[/B] (Radix := Binary);
	BIT Drive_Is_Enabled STATUS_WORD_1 : [B]15[/B] (Radix := Binary);
	INT JERK_STATUS;
END_DATATYPE
Hi PLCs.net! I'm using Studio5k V32, and I have an EDS file for the Fanuc 30r-ib plus controllers. I have an excel spreadsheet with bitwise...
1,447
Answered my own question. Didn't realize it was already under the controller Tags section. Sorry couldn't figure out a way to delete the topic.