Hello, I recently got my hands on a moeller ps4-341-mm1, I do not understand this plc it won't boot.

In the manual on page 65 says "The Run” and “Not Ready” LEDs will flash if the PLC does not have an operating system, and the PLC is in boot status."

I connected the PLC on the PC, I can't really get more information it's still say It's stuck in boot.

"ECM OS40-300 destroyed stop"
I do not have a memory module.

What can I do from here? all I see is this thing is better off to go to the trash.
 
You cannot pull programs out of these PLCs so you don't need to try anything there.

Starting the PLC is usually 2 step process. If I remember correctly, there is a three position rotary switch and a pushbutton. Rotating the switch sets up what will happen when you press the button. these are under the door on the right of the base unit.

So you can try to move the switch to 2-Run and then press the button and see if it goes into run mode. Or 3-Run M-Reset (resets retentive data to defaults) and press the button.

If you don't have the software and/or cables it's better to start over with new hardware. These controllers are very obsolete.
 
Thank you for trying to help. Nothing worked at this point it's a lost cause, I just wanted to see if I could maybe get this working. I'll just sell it for parts and I have 3 modules with it.
 

Similar Topics

Hi group, We have a bit of an issue which I am sure you guys have heard before, I did look at the previous threads but could not see if there...
Replies
0
Views
540
Hi, First i'm a beginner and not a very good in english so i will try my best to be clear ! I work on an used installation and me and my team has...
Replies
0
Views
673
Hello, I have a client asking me to move a program from a PS4-341-MM1 to another one. I have the cable and the Sucosoft 5.0 program. My question...
Replies
0
Views
829
Hi Guys, So we have several machines with PS4-341-MM1 controllers. We use the ZB4-901-SF2 memory module. We do not have source files. We have 4...
Replies
5
Views
2,427
Hi I conected the PLC Moeller PS4-341 and Siemens modem TC35i over ZB4-501-UM4,I downloaded the sample from Moeller site ( the sample is made for...
Replies
2
Views
5,020
Back
Top Bottom