Monitored dump valve wiring
Kevin1793
Dec 2018
San Luis Potosi
Hi everyone!
I'm working on the controls design of a semi-automatic pneumatic vertical press. The machine will consist of two double-acting cylinders with 5/3 closed center valves and pilot-operated check valves on cylinders ports to keep them in position when no power is applied to the solenoids. Everything controlled by a non-safety PLC to automate the operation. An e-stop, light curtains and a dual dump valve hard-wired to safety relays (all dual channel) with auxiliary force-guided relays will be the safety devices.
The dual dump valve is a SMC VP544-X538 and has 2 safety limit switches for detection of the main position of the valves. I want to use these limit switches to achieve redundancy. Since I don’t have a programmable safety relay, can I wire them to inputs of the non-safety PLC?, or should I wire them to a safety relay? How is the logic that must be implanted for these switches?
I’ve attached a simple diagram illustrating the safety circuit i got so far to see how can I add them to my safety circuit. Any help will be appreciated.
feedbackcircuit of E-stop-safety relay
in series with NC of main-contactors
purpose:
check if dumpvalve's and contactors are both in off-state
before reset of E-stop.
purpose:
Thank you.
One more question. Then isn't necessary to use the other NC contact of the dump valve's limit switch to achieve redundancy?
In OB1, I'm monitoring some values (first pic). The values are what I expect. At the same time, I'm monitoring the same values in the DB where...
665
Dear All, new to rslogix 5000...suppose i build add on instruction to start a motor. use that for 10 different drives. Is it possible to...
2,946
Hi everybody, I'm programming a routine in RSLogix 5000 for a regulation level in a tank. I'd need to monitor the increase / decrease of such...
3,334
We just had a sub (node) lose communication on our DH+. My co-worker mentioned that this might be due to the # of RSlogix applications that were...
3,421
I have a micro1400 processor running two routines (transfer compression/compression molding press). Recipe parameters are stored from job to job...
61