Motor Contactor

Hey everyone, thanks for all of the info. To answer a few questions,

The contactor is a Cutler-Hammer 15Amp @ 600V, The pressure switches monitor the screen deck pressures (Hydraulic) this motor runs the infeed conveyor and is strictly electric. When the pressures in the hydraulic circuit get too high, the pressure switches are suppose to drop the contator out and shut off the infeed conveyor thereby preventing a more severe plug up.

This is a bit of a bastardized sysstem, components having been added over time. The last electrical company was the one that put this new contactor in, I have purchased a new one and will be installing it in the morning. I will keep you all posted.

Thanks,

Willpower
 
Jolio,

It would have caused a lot of problems and damages if not for the good use of fuses. 25 fuses had burnt from that one fault.

Normaly you should look at selectivity of your fuses. When you have a short circuit only one fuse should go out not 25!!!

What I also trying to do is split up the short circuit protection and the overload protection.

Rudi
 
Rudi

The whole row of relays in plastic dust cover have faulty coils and contacts that are jammed up. This causes a few short circuits.
Quoting myself :D , The one fault I meant was the faulty relays. there are 25 faulted relays so it caused about that much shorts, and blown 25 fuses.
This panel already has overcurrent relay, over/under voltage relays, reverse power relays etc etc.
The whole console looks like it's plucked out of "Star Trek Enterprise" show. lolis

regards
Sherine T.
 

Similar Topics

I have a customer request that reads (slightly edited) Smart Motor Contactor This will monitor incoming power for irregularities in voltage...
Replies
7
Views
2,423
Hi folks, I know this is off-topic, but I'm sure someone will know this. I have an older machine with a 3 phase 208 VAC 10 HP pump motor that is...
Replies
16
Views
4,331
So, ran across a part today that I can't really figure out where it would be used. Its a 4 wire contactor with a NC circuit, when you power the...
Replies
10
Views
2,817
I have an old turret lathe, it has a dual speed motor operated by an old Square-D NEMA1 contactor, which have failed. The original contactor...
Replies
15
Views
3,827
Hi to all. My problem is basically a electrical problem. I have to "ON" a 3 phase motor via two contractor coil. But how it can be done in...
Replies
18
Views
5,794
Back
Top Bottom