Motor delays
Welcome to the PLCTalk forum !
This sounds, of course, like a homework question. And it's tradition here to put the most effort into students who show their work or explain their thinking.
I would use a self-resetting Timer instruction whose Done output added 1 to a counter every time it completed a cycle.
The value of the counter would then be compared to a constant (1,2,3,4,5,6) on a rung that controls the motor starter.
Additional aspects you might want to think of:
1. What starts the sequence: a pushbutton, or an HMI, or an event in the PLC ?
2. Can the sequence be stopped before it completes ?
3. Should you confirm that each motor has started, and not proceed with the sequence if one stalls or fails to start ?
4. Should the operator be able to stop the sequence in the middle ? Should all the motors stop if the sequence is stopped, or should just the ones that have already started keep running ?
5. If the sequence is stopped, what happens when you start the sequence again ?
Something that sounds very simple in theory can get much more complex when you consider all the possible failure, interruption, and restart modes.
Again, welcome to the PLCTalk community !
Thank you for the quick reply. Yes you are correct, homework question! But just a push button to start the sequence. And a push button to stop once all motors are running. Interuptions or anything like that doesn't matter.
Well, then show your work so far, even if it's just how to make a pushbutton start a repeating timer.
If you are programming for a particular PLC make and model, let us know so that we can use the appropriate memory addressing syntax and instruction set.
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
49
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
296
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
156
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
357
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
221