I know the torque of an Induction motor. Now I need to calculate the current. What is the best way to do it so that it can express in software ? I have seen , Current = torque * 1/(torque constant) * gravitational acceleration . Could anyone clear me what is gravitational acceleration ? Also how to find out torque constant ?
 
You will need to know the magnetizing current of the motor. It is the actual current drawn when the motor is at no-load. Or, the manufacturer can provide it. And you know the full load amps from the motor nameplate.

Set up a vector triangle with the magnetizing current on one side and the full load current as the hypotenuse. Solve for the remaining side which is the full load torque producing current.

This is the torque producing current at full load torque. It is directly proportional to actual torque. So, given the actual torque, find the actual torque producing amps. Using the Pythagoreon Theorem again, use the known magnetizing amps as one side, the actual torque producing amps as the other side, and solve for total amps (the hypotenuse). That is the total amps under reduced torque conditions.
 
I usually just get the motor data sheet. It will usually provide amps at full, 3/4, 1/2 and no load.

Gravitational acceleration "g" is 32.2 ft./s/s or 9.81 m/s/s on this planet.

I think you are getting yourself into a calculation more complicated than you need, and usually g doesn't enter into the kind of calculation you are doing. What exactly are you trying to accomplish?
 

Similar Topics

Kindly, has anyone tried to control Lenze servomotors with Siemens S120 drives ? Any special hints ? Have some concerns for the resolver and servo...
Replies
5
Views
234
Hi all!!! Anybody ever seen this code on this motor drive? Can't find any references for it in any manuals!!! Sorry I know it's not PLC, but...
Replies
0
Views
739
hi goodday to all, i have acopos 1320 as below title my acopos not driven a servo motor,. please help me,.
Replies
0
Views
444
Hi all, I have a powerflex 525 where there is no voltage coming out to the motor. The drive was reset to factory defaults with stop and saftey...
Replies
13
Views
2,774
I inherited a project with lots of problems. They are using a small motor, 12/24v, 6A and are so far along the motor is a given. I am looking...
Replies
20
Views
5,584
Back
Top Bottom