basharath Member B Join Date Mar 2010 Location hyderabad Posts 103 Nov 3, 2010 #1 we have motor run feed back and trip fedback..from where do we take this feedback from the field. thanks.
we have motor run feed back and trip fedback..from where do we take this feedback from the field. thanks.
IJK Member I Join Date Sep 2010 Location pune Posts 67 Nov 3, 2010 #2 The Simplest way is use contactor contacts for run feed back in the panel it self. or u can use an MPCB which will provide u trip feedback.
The Simplest way is use contactor contacts for run feed back in the panel it self. or u can use an MPCB which will provide u trip feedback.
Tom Jenkins Lifetime Supporting Member Join Date Apr 2002 Location Milwaukee, WI Posts 6,302 Nov 3, 2010 #3 Most starters have auxiliary contacts on the starter contact and the overload for status indication. I usually use NO for Run and NC for overload. For some less expensive IEC starters you will have to use adder blocks for the auxiliary contacts.
Most starters have auxiliary contacts on the starter contact and the overload for status indication. I usually use NO for Run and NC for overload. For some less expensive IEC starters you will have to use adder blocks for the auxiliary contacts.
Jeff23spl Member J Join Date Jan 2010 Location Canada Posts 860 Nov 3, 2010 #4 our standard is to have the overload NC connected to release the contactor coil when tripped and the NO signal the plc of overload trip
our standard is to have the overload NC connected to release the contactor coil when tripped and the NO signal the plc of overload trip