Hi,

I almost always use a fused disconnect for enclosures, usually class J and rely on the Bussman SPD publication to help with sizing the appropriate fuses for the disconnect sizes, since I mostly (99% of the time) deal with motor control.

Is there a trusted publication for Molded-case circuit breakers that is similar or a sizing chart? We have a customer that is requiring a circuit breaker for the main disconnect rather than fuses.

I've found this schneider electric one:
https://www.se.com/us/en/faqs/FA239478/

but it seems to be all I've found thus far. If anyone has a great resource, please share!
 
Personally I would consider rather using a properly sized manual motor overload

This one from FactoryMation.com is $32 and they have a range of settings from 0.1 to 65 amps.
 
I didn't find a better table, but I guess I should have looked closer at the NEC.

NEC 430.52 has the inverse time circuit breaker % at 250% with the time-delay fuses at 175%. Doing the math, the numbers all add up to on the above chart.

It appears NEC 670.4(c) mentions the size could be for fuse OR circuit breaker, so the main disconnect size would use the same calculation as the fuse.
 
Last edited:
Years ago most of the motor control mfrs gave away (for free!) what were called "slide charts" where you slid a center core chart to the appropriate motor HP, picked out your voltage, and the chart displayed the motor starter, breaker, fuses and OL heater elements for you. haven't seen one of those in years now though...
81LzWlhtW7L._AC_SX679_.jpg

But apparently you can BUY one on Amazon...

What a world...
 

Similar Topics

I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
286
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
149
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
350
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
Replies
2
Views
218
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
1,044
Back
Top Bottom