Motor on PF755 vibrates at standstill
taylor1982
Aug 2011
Bavaria
78
Hi all,
I have a 100hp torque motor running on a Powerflex 755 drive. The motor is coupled to a drum which is accellerated and decellerated.
The problem now is, that the drum start to vibrate when the drive is enabled and get set speed = 0. This happens not every time and when you turn the drum manually just a bit then the vibrate is gone.
Has anybody hints what could avoid this vibrations? I did the Autotune with the drive an all other functions are fine.
Thank you
Steve
Do you still have run 'run' high when command is 0 ?
Yes, actually the run is always high and i just manipulate the reference speed. Of course a FALSE on run would help but are there any solutions that would avoid the vibrations even when drive is in control mode?
Is the control 4 to 20 mA or 0 to 10V etc ?
There maybe tiny variation in plc signal or noise like emc causing the drive to pick up a speed reference. Does the vibration go away if you disconnect the speed reference
Been a while since I worked with this drive. If I recall correctly you could use the Sleep/Wake parameters [351-355] to limit movement until a minimum reference level [Volts or Current] is reached.
I completely control the drive with Ethernet/IP. I think it has something to do with the drive‘s internal management when in control mode and Target speed 0.
Maybe it toggles between encoder increments and that causes this vibration around standstill speed. The motor has an 2048 increment encoder.
Thanks for that hint! I will have a detailed view on that parameters the next days and will give feedback.
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
205
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
306
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
158
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
361
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
223