Hey guys.
So I have a 50 HP 460/600V motor on a PF525. I've verified the motor is wired correctly. The service factor is 1.15 and the pf is 0.8 The name plate states that for 460 it should be wired in delta, and it's FLA is about 52A. They are trying to run it at 80 Hz, and getting an overcurrent condition. The current is also not a stable current. It the magnitude oscillates.
They can run it at 80% and it runs at about 50A, which makes sense. I can definitely smell the windings cooking when I open the JB. I've megged the motor and wiring, and they seem to be okay. It's been tuned.
This is new equipment custom built for us. I've asked for the motor sizing calculations to review them, but it's not likely I'll get them. I do suspect it's undersized, as at 60 Hz it pulls it's FLA when being ran.
I checked the fault logs and didn't see any kind of over-current or overload faults. People are leaning towards it being a bad motor, but I'm also wondering if it can be a bad drive / potentially be misfiring. I'm not sure how to check that out.
The drive is fed with shielded VFD cable, and the shield wires are clamped to a grounding bar prior to landing on the drive. There is no line reactor or output choke.
I feel like there might be some stuff to try, but I don't know what it might be at this point.
So I have a 50 HP 460/600V motor on a PF525. I've verified the motor is wired correctly. The service factor is 1.15 and the pf is 0.8 The name plate states that for 460 it should be wired in delta, and it's FLA is about 52A. They are trying to run it at 80 Hz, and getting an overcurrent condition. The current is also not a stable current. It the magnitude oscillates.
They can run it at 80% and it runs at about 50A, which makes sense. I can definitely smell the windings cooking when I open the JB. I've megged the motor and wiring, and they seem to be okay. It's been tuned.
This is new equipment custom built for us. I've asked for the motor sizing calculations to review them, but it's not likely I'll get them. I do suspect it's undersized, as at 60 Hz it pulls it's FLA when being ran.
I checked the fault logs and didn't see any kind of over-current or overload faults. People are leaning towards it being a bad motor, but I'm also wondering if it can be a bad drive / potentially be misfiring. I'm not sure how to check that out.
The drive is fed with shielded VFD cable, and the shield wires are clamped to a grounding bar prior to landing on the drive. There is no line reactor or output choke.
I feel like there might be some stuff to try, but I don't know what it might be at this point.