Hey guys.


So I have a 50 HP 460/600V motor on a PF525. I've verified the motor is wired correctly. The service factor is 1.15 and the pf is 0.8 The name plate states that for 460 it should be wired in delta, and it's FLA is about 52A. They are trying to run it at 80 Hz, and getting an overcurrent condition. The current is also not a stable current. It the magnitude oscillates.

They can run it at 80% and it runs at about 50A, which makes sense. I can definitely smell the windings cooking when I open the JB. I've megged the motor and wiring, and they seem to be okay. It's been tuned.

This is new equipment custom built for us. I've asked for the motor sizing calculations to review them, but it's not likely I'll get them. I do suspect it's undersized, as at 60 Hz it pulls it's FLA when being ran.

I checked the fault logs and didn't see any kind of over-current or overload faults. People are leaning towards it being a bad motor, but I'm also wondering if it can be a bad drive / potentially be misfiring. I'm not sure how to check that out.

The drive is fed with shielded VFD cable, and the shield wires are clamped to a grounding bar prior to landing on the drive. There is no line reactor or output choke.

I feel like there might be some stuff to try, but I don't know what it might be at this point.
 
52 amps sounds like a 40HP motor.

30HP PF525 is rated 43 amps.

Depends on type of motor and what the load is.

Similar situation on a small extruder. 22Kw A-B motor. The load is fairly high, so ended up with a 40HP PF755. Been working well for the past 6 years. Next is to upgrade controls and remove all the Dnet, SLC500 stuff. Actually use a real E-Stop system. LOL
 
Can you post a photo of the motor nameplate?


Yea I'll get one. I did another retrofit to go from a soft start to a drive yesterday under a lot of pressure and I think I'm conflating the two.


It's actually a 700 series drive. I'll get the info from both in a bit.
 
Yea I'll get one. I did another retrofit to go from a soft start to a drive yesterday under a lot of pressure and I think I'm conflating the two.


It's actually a 700 series drive. I'll get the info from both in a bit.




That will help.
 
A couple comments.

All motors we use, WEG and Baldor, state that the service factor is 1.0 when run from a VFD. Even if the across the line SF is 1.15.

At 80Hz you are well into the constant HP region of the drive operation. Your torque capability at 80Hz will be about 75% of what it is at 60Hz. What is the application?
 
If the windings smell cooking or burning, it is very likely that there are some short circuits between turns.
 
Here is the nameplate. Forgot to get it last night. Had someone on site get it today. Sorry it is kinda blurry. I also got the VFD label. Just looking at this, though and given that it's wired for 460 delta, it looks like we are maxing out the drive.


I can't quite read the kW from the pics so I asked him to confirm it. Sure looks like a 60 to me, but surely not. That would explain the oscillations with the current though.


EDIT: Got them to confirm it's a 40 HP, so that must be a three.




LkRowjg
LkRowjg
LkRowjg



 
Motors are amazing, they will work themselves to death if you ask them to. This is why we have to make sure the overload protection (Heater, bi-metallic strips, electronics, whatever) are sized absolutely correctly to the motor, not the load. If the motor cannot move the load, then either the load is too big or the motor is too small.

A motor working itself to death has a very distinctive smell, like burning money.
 
Max rpm is a function of frame size and number of poles. 80 Hz on a nominal 750 rpm motor should be OK, but prudence dictates you check with the manufacturer.

You haven't answered nOrM's question about the application, which is crucial. Above nominal speed most VFDs are capable of operation at constant motor power. That means the torque capability drops. You need to determine the power demand and torque demand of the load at speeds above nominal.

Frankly, this looks like insufficient application engineering, not a bad drive or a bad motor. Just sayin'.
 

Similar Topics

I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
187
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
141
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
341
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
Replies
2
Views
208
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
1,018
Back
Top Bottom