I think you have a choice of using one VFD as a master to drive the other two at the same frequency OR you can use the PLC to send 3 speed signals one each to each of the VFDs.
If you go with the VFD master then they will all be at same frequency the only variation between them will be the slip. So if you can live with each one speed varying by say 5& you are OK.
The PLC option lets you set a specific speed for each VFD and motor ie the input multiplied by some factor to give different speed signals to each VFD.
IN either case
You will not get fine speed control ie cannot control for slip under varying load conditions and will have to live with any slip thus each motor gearbox varying a little unless you go with encoders to measure actual speed and feed that back to result in real fine speed control.
Dan Bentler
If you go with the VFD master then they will all be at same frequency the only variation between them will be the slip. So if you can live with each one speed varying by say 5& you are OK.
The PLC option lets you set a specific speed for each VFD and motor ie the input multiplied by some factor to give different speed signals to each VFD.
IN either case
You will not get fine speed control ie cannot control for slip under varying load conditions and will have to live with any slip thus each motor gearbox varying a little unless you go with encoders to measure actual speed and feed that back to result in real fine speed control.
Dan Bentler