MOV copies just one word of data and converts between data types. eg, a DINT 100 moved to a REAL is converted to 100.0
COP copies multiple words of data and performs and exact bitwise copy of the data. Since there is no data type conversion a DINT 100 COPied to a REAL becomes 1.4012985e-43 (Which can be very useful)
In Allen Bradley a MOV interprets the source as a numeric value then sets that numeric value into the destination. If it is a float to an integer it will truncate the value.
A COP copies the bit pattern of the source into the storage space of the target without any attempt to interpret it as a value. So COPying between different types can be risky if you don't know what you are doing.