The application I have running sends a Modbus message to a scale head to find out the weight. The message results are stored in N12:60 for 4 elements.
Then taking N12:63 and moving it to N7:3, leaving the rest behind. Somehow this seems to get around the 32767 limitation and it reads instead in Hex format and does not fault out with an overflow error.
However I want to take 3 of these readings, combine them and put them into another register (N15:30) so I can send this information to a server piece.
No matter how I try to do this it will not work or be accurate.
I have tried the following:
ADD N16:3 and N16:4 result into F8:1
ADD F8:1 and N16:19 result into F8:2
MOV F8:2 into L22:0
CPW L22:0 into N21:0 (for testing purposes) length of 2.
Result I get is N21:0 is not the number or even close and N21:1 is 1
I'm sure there's plenty more information needed but I thought you could have a look and see if we can get the ball rolling on how to solve this.
Issue is it is for a scale that reads up to 65,000 lbs. I wand to combine 3 of them and report the total number.
Maybe it's just me, but I'm having a hard time tracking with you. For the sake of simplicity:
1. What format does the scale weight data come into the PLC (signed integer, unsigned integer, BCD, etc.)?
2. How many bytes/bits make up the scale weight data?
3. If you transpose the data bit for bit into a long integer (using say a BTD), does the data display the correct weight?
4. Are you saying you want to take three readings from the same scale and then find the average weight?
Take a big step back and look at the N12:60-63 elements in Hex format, and consider what they're supposed to represent.
This is a very common problem when Floating-Point data is packed into Modbus memory registers.
CPW and maybe BTD or SWP are going to help you solve the problem, but let's figure out what's supposed to be there (and the hex values) first.
Ok, in Hex format they are as follows:
N12:60=0 N12:61=19 N12:62=0 N12:63=561D
Negative. What I need to do is take the reading that is coming in via Modbus and add 3 separate scales, total them up and report that number in an integer to send to the server.
A little more specifically what my problem is...
I have 3 different PLC's getting weight information from the scales via Modbus TCP. This is being put into registers and the weight is being taken from them and transferred to another PLC which then transfers all that information to yet 2 more. I need to take 3 of those weights at the end and combine them into 1 total weight.
The message already in place is using N registers to send data in a MSG to the server. I just need my total number in one of those existing N registers already going to the server.
OK, so your weight comes in two words (word 3 = MSW, Word 4 = LSW per your attachment). If you copy those two words into a Long integer, you should get the weight in one register. If the value is incorrect, you will need to do some byte swapping to get the right value.
I'm not real familiar with MicroLogix but it seems to me like you'd be best suited doing your addition in L registers as this won't involve any more manipulation than what's mentioned above.
Can you use L registers for this? Sounds like this would be the most straight forward since the total weight could be > 65536.
How are you going to put a number > 65536 into ONE N register? If you're willing to sacrifice resolution, you could store the weight in 10's, 100's, or 1,000's. of pounds.
This is what I'm trying to understand myself.
First problem I have is that the scale data is being input in an N register, well 4 of them to be exact but then the weight is being taken from one register and moved to another. HOW though is that value being represented as a Hex value and not a decimal value right away in the table?? I just tried writing the EXACT same message on another ML1400 on the system and it instantly puts the values as a decimal value into the tables. If I can work with Hex values instead it's not a problem.
I am trying to figure out how they did it to begin with.
Provide some sample data and we can figure it out. Several examples of:
This is what the scale says, and this is what the 4 registers in the PLC say.
This is what I provided before:
Along with this the scale reads: 22045 at this point.
0x561D hex = 22045 decimal, so the data is coming in as an ordinary integer instead of a floating-point value.
Do you know if the datatype is supposed to be a 32-bit signed or unsigned integer (spread across N12:62 and N12:63) or a 16-bit unsigned integer (in N12:63 only) or a 16-bit signed integer (in N12:63 only) ?
The easiest thing to do, I think, would be to use a CPW instruction to move the hex data unmodified from N12:62 and N12:63 to a single L-type Long Integer register.
You can then do the addition and averaging with the Long datatype.
It's all pretty easy to do with Long or floating point, what I'm trying to figure out is how they did it all in N files and how to duplicate that process.
You need to figure out the datatype for certain. As I described, it's probably either a 32-bit signed integer or a 16-bit unsigned integer.
You can do that either by reading their documentation, or by increasing the transmitted value to larger than 32767 to see what the equivalent hex values in the two adjacent registers are.
I recommend against devising some sort of 16-bit unsigned integer workaround unless it's entirely necessary: a person who works on the system after you might not want to reverse engineer your workaround.
I'm having to make an AOI to use with a generic ethernet device because the manufacturer does not provide an AOP. I just want to do a sanity check...
1,265
I have found several places in an old program where COP of length 1 is used on strings, but other places where MOV is used. Is there an different...
4,019
Why not use CPS for everything? When would you actually want to allow the data to change during the copy operation?
36,773
Would someone be so kind as to explain the difference between the cop, mov and cop instructions and where each one may be used? The instruction...
5,944
Can someone tell me the difference between these two instructions and where you would apply one vs the other? Thanks
4,635