MSG Instruccion
alondra007
Oct 2008
Lake Mary, Fl
18
Can some one explain me how the MSG instruction works.
I want from a SLC500 5/04 pass the value of a Float F8:0 to another slc500 5/04 F12:0.
I don't understand why i can't get this going, it can not be this difficult.
thanks,o_O
I'm taking a guess that the 2 PLC's are connected together via Data Highway ?
If so, there's two ways you could do it:
1. A Message Read instruction in the F12 SLC to read the data from the F8 SLC.
2. A Message Write instruction in the F8 SLC to write the data into the F12 SLC.
Look up the MSG instruction in the online help for more information.
Like Sergei said, we would need to see your PLC program - or at least some screenshots of how you have the MSG instruction set up, to help you any further.
below is the screen shot of the MSG read. Yes it's thru DH+. This is on one of the slc 500 5/04
The value i want is on F8:0 and i want to pass it to F12:0. I get an error Hex(15).
Error 15H is a channel configuration error. Check each controllers DH+ channel configuration to make sure the baud rate is the same and the node address is different. As requested above it would be best if you could post both controllers .RSS file for the best help.
I built 3 5/04 trainers for a customer... attached is the programs with a MSG from (I think) node 2 to 4, they wanted an example... nothing fancy but it may help
Your MSG instruction looks OK. Like Mickey says, it appears to be an error in the DH+ connection between the 2 SLC's. Check the Channel 1 settings in each PLC.
Are these SLC's just connected to each other - or are they part of a larger DH+ network ?
Are there any other MSG instructions in either SLC ?
122
I have an 1769-L16ER that I use to test code and I just found that I can't create MSG tags at the local program scope - they have to be done at...
211
I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
201
I'm trying to read/write to an SLC5 with a ControlLogix L71 V35 plc that fails. The exact same code works on an L82S with V32. Is there a known...
312
Hello all, I am currently trying to establish a message instruction to pass data from a 1756-L73 to a 1756-L71. My communication path from the...
385