multiple 1794-asb with 1756-dhrio question
lunknowl
Oct 2012
vietnam
37
hi i try to setup 6 1794-asb to a 1756-dhrio channel B. do anyone know how to adjust the dipswitch of the 1794-asb module ?. i already look at the manual but it doesnt mention about 1756-dhrio. thanks
do you read my question because answer it? stop provide stupid manual i already read it and nothing mention about 1756-dhrio.i can use the 1747-sn but it only have 0-3 number of rack!anyway it you dont know it stop support
I think that you confusion is that the table on Page 2-11 of the 1794-ASB user manual does not list the 1756-DHRIO as a scanner.
It shows the 1747-SN, the PLC-5, the PLC-5/250 and the PLC-3.
That does not mean the 1756-DHRIO and 1794-ASB are incompatible. The DHRIO simply isn't listed in that old manual.
The 1756-DHRIO has two channels that can be configured either for DH+ networking or as RIO Scanners.
Each channel configured as a RIO scanner can support up to 32 physical devices, with up to 32 "logical rack" numbers.
The Rack Numbers are in Octal addressing, and the 1756-DHRIO supports the full range of 00 through 77 (like the PLC-3 did).
If you have six 1794-ASB modules, the simplest thing to do is set them up as "rack" numbers 00, 01, 02, 03, 04, 05.
thanks for support, the 1756-dhrio support full range but for the 1794-asb manual the rack dipswitch doest not list 1756-dhrio like you mention so i have the question of dipswitch of 1794-asb ( i dont know if i can setup as same as PLC-5 BECAUSE THE 1747-sn setup only support for 3 rack)
I think a apology is called for lunknowl. You were pretty rude to a member that helps many here and gave you the correct info.
Yes, you can consider the 1756-DHRIO to be similar to a PLC-5 or PLC-3 controller. It does not have the 4-rack limitation of the 1747-SN.
The RIO protocol was introduced in 1978, so there are a very large set of Allen-Bradley products that use it. Their documentation literally spans decades of time, and may not be perfectly updated and consistent.
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
58
is it possible to install multiple ibaPDAs on single VM or PC?
40
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
78
141
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
90