Multiple HMI terminals for Ignition deployment

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
With Wonderware, IFIX, FactoryTalk View, etc., it's very easy to have multiple HMIs, each with their own independent control, looking at the same HMI application. I'm assuming the same can be done with Ignition with relatively easily? I've only played around with it lightly thus far.
 
Yes, each one just needs to install the Client Launcher and your license needs to support the number of Clients you are going to run simultaneously.
 
Ignition has two visualization modules. Vision is more like a conventional hmi system that can be licensed with unlimited clients or on a per client basis. Perspective is HTML based and doesn’t use clients. A browser connection is all it takes so it isn’t limited in that sense. You can purchase a license for your gateway with either, both, or no visualization module. Their site explains it in detail.
Not a rep. Just a satisfied user.
 

Similar Topics

Hi everyone I'm looking for some help with a problem please. I have a Siemens S7-1200 and 3 off KTP900 HMI's connected on the same Profinet...
Replies
7
Views
1,958
Having a hard time getting the data received when using BeginReadMultiple. Not the most familiar with the ClxDriver and EthernetIPforCLXCom()...
Replies
8
Views
2,326
Hi, I've got a new project for a vacuum conveying system. We require to add another HMI to the existing system which will then feed 2 separate...
Replies
6
Views
1,829
Hi, I have been successfully sending emails from a Siemens Comfort HMI (TP1200), configured with a "Gmail" address via VB Script. The VB...
Replies
6
Views
2,280
Hi fellas, Hoping someone can help me get started with this. I'm a little out of my comfort zone trying to set up communication with a ProFace...
Replies
0
Views
834
Back
Top Bottom